    Daikin Multisplit 4MXS80E high current



    Daikin inverter 4mxs80E with 2 x 2,5KW innside units (4mxs80E2V3B, FTXS25G2V1B, FTXS25CVMB8)
    Problem : always high amp draw (approx.18 amps), compressor the same frequency in forced mode as when 1 or 2 units on.
    I cannot find out if it is the compressor or the PCB!
    I already know that it's not under or overcharge.

    What should be the current draw when in forced cooling mode ?

    In heating mode the compressor works perfect, its frequency lowers (very silent, also the fan lowers in frequency)

    Thanks for helping!
    JRS



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin Multisplit 4MXS80E high current

    Compressor frequency depend on some inputs. If one of those inputs are wrong, than control is wrong.
    I would start with checking thermistors which deal with cooling control.

  3. #3
    Join Date
    Aug 2013
    Location
    Netherlands
    Posts
    7
    Rep Power
    0

    Re: Daikin Multisplit 4MXS80E high current

    Hi,
    I checked all thermistors they are ok...

    In the manual is written that you have to connect a minimum of 2 inside units.
    Is this because of a minimum rpm output of the compressor in cooling mode?
    If you turn on one unit then the cooling works so why a minimum of 2 units?

    I tried to fake some sensors (heating up the discharge pipe thermistor) but nothing happens. Should lower the rpm I think.
    Is 55hz already the minimum rpm of the compressor when connected to 2 inside units 2,5KW?

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin Multisplit 4MXS80E high current

    Sorry I am not that familiar with Daikin multi splits.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin Multisplit 4MXS80E high current

    in cooling mode ur compressor current is always less,as is your maximum frequency18amp is way too high, is your reversing valve ok as u say it works ok in heating but runs flat out in cooling, and u say the gas charge is correct

  6. #6
    Join Date
    Aug 2013
    Location
    Netherlands
    Posts
    7
    Rep Power
    0

    Re: Daikin Multisplit 4MXS80E high current

    Thanks for the replies.
    Iam going to replace the compressor.
    Hope this is the problem.
    Will be back.
    Greetz
    JRS