    error 554 on Samsung UH070cav



    Hi guys! I got samsung EH070Cav indoor unit and UH070cav outdoor unit 1.5 years old. When i turn it on system works for 10 minutes and turns off with 554 error code.
    554 - Outdoor unit refrigerant Full leakage(Gas leak)
    I checked all pipes, valves for leaks and add a *****. But i have the same thing.
    May be the issue is in the pressure switch?
    Any ideas?



  2. #2
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    45
    Posts
    54
    Rep Power
    19

    Re: error 554 on Samsung UH070cav

    Check The Outdoor expansion valve - we have replaced many on the Samsung units - they seem to get stuck causing the compressor to overheat.
    Alternatively check strainer (on suction to compressor after the 4 way valve isn't blocked)

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: error 554 on Samsung UH070cav

    http://www.mediafire.com/download/3o...ice_Manual.pdf
    click on link above for manual- correct outdoor- but cassette indoor- no pressure transducer- either faulty temp sensor or compressor not pumping
    whats the standing pressure,running pressure, have you weighed out the charge to comfirm correct?
    are coils clean- indoor and out

  4. #4
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: error 554 on Samsung UH070cav

    outdoor PCB? maybe reading the wrong values from temp sensors
    Paul