MITSUBIHI CITY MULTY problem ... urgent !
Hi I am not specialist for MISTUBISHI VRF systems mostly working with DAIKIN and TOSHIBA .
So the system was working 5 years with no problems at all . After maintenance one indoor unit WALLMOUNTED PKFY - P20VBM-E start flashing check 015 6600 error code .( in top corner 1C )
Remote Controller PAR -20 MAA .
So I checked on Mitsi Web site faultcode its mean Ip address doubled . . . ???
Try to change for any different address and still doesnt work . Just still flashing with diferent address .
Replaced all three boards no help .
When disconnected another 4 units from communication its start working but that is not right solution ...
Please anyone know what could be main PROBLEM what should I do to working back all units correct ????
20130725_125740.jpg
Any advice much appreciated
Thank YouLast edited by Palkoper; 28-07-2013 at 06:31 AM.
-
28-07-2013, 10:11 AM #2
Re: MITSUBIHI CITY MULTY problem ... urgent !
whats outdoor model number?
is there a g50/central controller?
find all units on that system, log address- either at remote or on rotary dial on each indoor,then you should see a duplicate address, then reboot system
-
28-07-2013, 05:19 PM #3
-
28-07-2013, 05:30 PM #4
Re: MITSUBIHI CITY MULTY problem ... urgent !
http://www.mediafire.com/download/br...uhy200ymfc.pdf
city multi service manual- stufus is the dogs knackers on mitsi stuff