    Hitachi inverter fault



    Hi guys been called to a hitachi RAS-8FSG vrv system with a. Inverter fault 52 been to outdoor unit compressor start on start winding but dose not go to run winding trips out then P7 comes up on outdoor unit , dose any one know what this P7 mean on outdoor PCB
    thanks
    paul



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hitachi inverter fault

    http://www.mediafire.com/download/57...ITACHI_fs2.pdf
    click on link for service manual for a ras 8 fs- r22 inverter
    inverter compressors have 3ph to terminals- no run winding- on ras 8 - twin compressors- 1 direct online- and 1 inverter- within the same shell. if 1 comp is goosed then u can either disconnect dol or inv compressor and it will still run- p07 fault refers to reversing valve pressure diff strange- maybe ur pot aint pumping

  3. #3
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Hitachi inverter fault

    Cheers il check that out system is on R407c . It must be one of the first 407C it say it was made in 2000

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hitachi inverter fault

    hitatchi 407c manual
    happy reading- file is a bit bigger so will take longer
    http://www.mediafire.com/download/am...ne_service.pdf

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hitachi inverter fault


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •