    Suction / Discharge Pressures On RC



    Hi Guys ,

    I'm new to this game .

    I went out to service a split Ducted system Fujitsu Inverter AOT45LJBYL . After thoroughly cleaning the coils, filters etc I stuck my gauges on the unit . Standing pressure was about 1200 kpa . I turned on the unit and noticed that the suction was around 1900 kpa and the discharge was around 2000 kpa . ( only 100 kpa difference ) Is this normal on the reverse cycle with an inverter , Scroll compressor and a TXV ? I was lead to believe the TXV isn't used on the RC and I was maybe thinking the compressor was passing .

    I checked the 4 way valve to make sure nothing was crossing over and my true suction line back to the compressor was nice and cold and sweating .

    I checked the duct outlets and there was a 14 degrees C difference between return air and outlets. The customer never said he had had any issues with regards to lack of heat or cooling in the summer.

    With regards to checking the superheat and sub cool to see if it's undergassed do I check the pressure /temp on the gauges , then put my thermometer on the pipe going to the evap & true suction line as it's in heat mode ?

    Thanks Gordon



  2. #2
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: Suction / Discharge Pressures On RC

    If your main suction line is sweating perhaps the internal bi-metal over-temperature protection disk is leaking by internally in the compressor causing the pressures that you are seeing?

    http://www.emersonclimate.com/asia/e...p_overview.pdf

    http://www.youtube.com/watch?v=_D1OlE1yWoY

    As for checking the superheat here is some info.

    http://www.emersonclimate.com/Docume...re-article.pdf
    Last edited by passandscore; 22-07-2013 at 01:38 PM.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Suction / Discharge Pressures On RC

    First thing first...

    Where did you attach your gauge lines?

    To the two valves on the outside of the outdoor unit? If so you didn't see a discharge pressure...


  4. #4
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Suction / Discharge Pressures On RC

    Quote Originally Posted by The Viking View Post
    First thing first...

    Where did you attach your gauge lines?

    To the two valves on the outside of the outdoor unit? If so you didn't see a discharge pressure...

    hi viking

    are you thinking that he has put gauges to the suction and the liquid line?
    if so dont they say that the liquid line pressure should be the same or near abouts as the discharge pressure as its all on the high side.

    be nice to know as that is my understanding.

    thanks in advance

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Suction / Discharge Pressures On RC

    Also, being an inverter system the pressures do not mean anything unless you know exactly what the compressor is doing.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Suction / Discharge Pressures On RC

    No Moondawn,

    On a modern split the two interconnecting lines (and therefore the service valves) are normally intermediate pressure and suction pressure. True high pressure only exists inside the outdoor unit.

    All assuming the system is in cooling mode.


  7. #7
    Join Date
    Oct 2009
    Location
    Sydney
    Age
    38
    Posts
    69
    Rep Power
    15

    Re: Suction / Discharge Pressures On RC

    gbc,

    u live inaustralia, like me, where its cold. u had the unit on the heating cycle. did u check the pressures at the service ports on the exit of the unit? on heating the big pipe becomes the discharge, feeding discharge gas to the indoor unit, where it is condensed into liquid, and returns to the outdoor unit through the small pipe, (liquid line). most fujitsu inverters i have worked on have an electronic expansion valve (not a txv) located on the liquid line just inside where it enters the unit at the bottom right.

    so the pressures you
    are reading at the service ports are actually discharge pressure and liquid line pressure, which are both on the high side of the system. the 100kpa difference is simply pressure drop, through the interconnecting pipes, indoor coil and distributor.

    correct me if im wrong
    and u took your pressures somewhere else? but i reckon both your guages are on the high side....

    especi
    ally if u say the suction was nice and cold and sweating.... (which is an indication and ONLY an indication of a good superheat, and normal operation of the unit), and u had a normal air on/air off td....

  8. #8
    Join Date
    Jul 2013
    Location
    Australia
    Posts
    6
    Rep Power
    0

    Re: Suction / Discharge Pressures On RC

    Yeah your right enough , it was a electronic expansion valve on the bottom right at the back .

    I put the gauges on the 3 way service valves at the outdoor unit , and I do know the lines reverse when in heating mode and the larger pipe becomes the high pressure side .

    Yeah I should have maybe checked it in cooling mode to get a better feel of system pressures.

    Makes sense now that that would be a pressure drop . What's the air on air off td ?

    How would I get the true discharge on a system then , by measuring the temperature of the discharge pipe then cross referencing with my pressure / temp chart ? Most systems I have worked on only have the service port on the suction side .

    I need to get this superheat / sub cool thing right so I know when systems are under or over gassed as you said with inverters it's harder to pin point pressures as the compressor is ramping up and down

    thanks

  9. #9
    Join Date
    Oct 2009
    Location
    Sydney
    Age
    38
    Posts
    69
    Rep Power
    15

    Re: Suction / Discharge Pressures On RC

    u put your guages on the service ports? where the outdoor flares connect? on heating, they are both the high side.

    mate, a modern split system can be VERY hard to acturately diagnose refrigeration faults at times.... as u said, alot only have one service port, on the gas pipe (big pipe), especially the smaller ones. in this case, on heating that port is discharge pressure, and if there are no other ports u wont be able to get a suction. on cooling, this is reversed, with that port being suction, and you are unable to get a discharge pressure.

    from memory u will most likely find th
    at particular fujitsu unit will have a schroeder port or 2 inside the unit, its just a matter of tracing pipes to find out what pressures they will be. most split ducted systems will have more guage ports inside the unit, u may just need to take the cover off and have a look ​around to find them.

    disch
    arge and suction are constant ONLY to the reversing valve, after that they change depending on what mode it is set on....

    and no, u cannot take the temperature of the discharge pipe and use a pt chart to get the pressure.... discharge gas is highly superheated, pressure/temperature relationships only apply when a refrigerant is saturated (a mixture of liquid and vapour refrigerant) which occurs within the evaporator and the condenser.

    by air on/air off td, i was referring to the temperature difference between the air going onto the indoor coil and the air coming off the indoor coil, which you stated was 14k, which is good....

  10. #10
    Join Date
    Jul 2013
    Location
    Australia
    Posts
    6
    Rep Power
    0

    Re: Suction / Discharge Pressures On RC

    Thanks mate !