    ThermoKing V-500 max



    Can you please try to answer me one question. I am servicing thermo king V-500max, and I changed the ***** form r134 to r404. It is possible to change that parameter in a computer with a in cab controller? I have to change that because unit is shutting down because of the difference in the pressures of r134 and r404.


    Thanks for your answer



  2. #2
    Join Date
    Oct 2009
    Location
    Ireland
    Posts
    27
    Rep Power
    0

    Re: ThermoKing V-500 max

    Change the hp switch and cond fan control switch

  3. #3
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: ThermoKing V-500 max

    expansion valve is different as well.

  4. #4
    Join Date
    Jan 2010
    Location
    Slovenia
    Posts
    20
    Rep Power
    0

    Re: ThermoKing V-500 max

    Everything is ok. The computer was damaged so I had change it, but the software on a new computer was set tor r134. My system is working wit r404, so I have to change the parameter on a computer from r134 to r404. Probably I have to install new software on a computer.