Thread: ThermoKing V-500 max
-
20-06-2013, 03:28 PM #1
ThermoKing V-500 max
Can you please try to answer me one question. I am servicing thermo king V-500max, and I changed the ***** form r134 to r404. It is possible to change that parameter in a computer with a in cab controller? I have to change that because unit is shutting down because of the difference in the pressures of r134 and r404.
Thanks for your answer
-
20-06-2013, 10:30 PM #2
Re: ThermoKing V-500 max
Change the hp switch and cond fan control switch
-
21-06-2013, 05:19 PM #3
Re: ThermoKing V-500 max
expansion valve is different as well.
-
24-06-2013, 02:28 PM #4
Re: ThermoKing V-500 max
Everything is ok. The computer was damaged so I had change it, but the software on a new computer was set tor r134. My system is working wit r404, so I have to change the parameter on a computer from r134 to r404. Probably I have to install new software on a computer.