    High and low pressure cut off



    In R410a system, what is considered to be a good cut in and cut off for the high and the low pressure switch?



  2. #2
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: High and low pressure cut off

    what type system,air-cooled or water cooled,heat pump operation? the low and high pressure should consider the compressor permitted work range and system performance requierment. would u pls give some background?

    rgds
    LC
    I hear...I forget;I see...I remember;I do...I understand

  3. #3
    Seng's Avatar
    Seng Guest

    Re: High and low pressure cut off

    It is an air-cooled condenser for a commercial split system. I just need the normal range to start. Thanks for the help.

  4. #4
    Mushtaq Kumbay's Avatar
    Mushtaq Kumbay Guest

    Re: High and low pressure cut off

    check the condensing temperature on your 410a gauges and set it at about 20c degrees above the condensing temp

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: High and low pressure cut off

    Hp is related to the max allowable pressure of our compressor
    If temperature can rise to 32° ambient with a DT of 14 K, then 28 bar and 9 bar DP.
    LP 7 bar cut in and 2.5 DP if it only needs to cool in summer.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.