    old mitsubishi 12 rv a2



    having some problems with this unit, i have been told the voltage across terminal 1 and neutral should be around 9>12 volts d/c. when i checked i found had 20>22d/c. was told by tech support to replace faulty indoor board. Installed new board still the same. i get 240 volts on terminal 2 (supply to outdoor) for a few seconds then unit faults. the green lights just flash.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: old mitsubishi 12 rv a2

    is the transformer external from the board? if so check outputs- as you say its a 12v dc signal on 1,2 for cooling,and 3 energises reversing valve

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: old mitsubishi 12 rv a2


  4. #4
    Join Date
    Apr 2010
    Location
    australia
    Age
    45
    Posts
    78
    Rep Power
    15

    Re: old mitsubishi 12 rv a2

    the transformer is built into the board, cant see the voltage on the transformer. the compressor relay on the board (indoor) has 12volts d/c coil. could there been something causing the higher voltage?

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: old mitsubishi 12 rv a2

    is the 12v transmission cable run parallel with any mains cable