    Is a Potetial relay position sensitive?



    I didn't see an arrow or the word TOP on it so I figure it doesn't mater. What say you?
    Ken



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Is a Potetial relay position sensitive?

    Well, I did a quick search on Google and most of them said " multiple mounting positions" then I found this - so now I'm not sure http://relays.tycoelectronics.com/da.../38_Series.pdf

  3. #3
    Join Date
    Feb 2006
    Location
    Calgary, Alberta
    Age
    66
    Posts
    13
    Rep Power
    0

    Re: Is a Potetial relay position sensitive?

    Yes, potential relays are position sensitive. Each must be calibrated for the position it's to be used in. By installing one in an incorrect position, you risk, altering the Pick up and Drop out voltages.
    Rick

  4. #4
    vEStMaN's Avatar
    vEStMaN Guest

    Re: Is a Potetial relay position sensitive?

    Hi,
    P.relays usually sit in the upright position they are gravity assisted to switch over from start to run,lying them down (connections at the top) inhibits the cross over, causes the relay to stay in start position thus burning out the start windings.

  5. #5
    Join Date
    Feb 2006
    Location
    ct
    Posts
    11
    Rep Power
    0

    Re: Is a Potetial relay position sensitive?

    depends on make of relay
    for instance copeland oem relay is position sensitive but an aftermarket such as mars is multi positional

  6. #6
    Join Date
    Feb 2006
    Location
    ct
    Posts
    11
    Rep Power
    0

    Re: Is a Potetial relay position sensitive?

    usually the cheaper relays are position sensetive which is the reason compressor manufactures love them

  7. #7
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: Is a Potetial relay position sensitive?

    This partiular relay came with a Danfoss factional hp. ( no markings) with a start cap and run cap.
    Ken

  8. #8
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Is a Potetial relay position sensitive?

    Quote Originally Posted by kengineering
    I didn't see an arrow or the word TOP on it so I figure it doesn't mater. What say you?
    Ken
    IT's position sensitive and normally closed

  9. #9
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Is a Potetial relay position sensitive?

    I didn't know potential relays sensitive to position. Dang, all these years. Seems most are mounted spade up, but I recall hundreds mounted on the back wall and at other tilts.

  10. #10
    Join Date
    Feb 2006
    Location
    ct
    Posts
    11
    Rep Power
    0

    Re: Is a Potetial relay position sensitive?

    if it came with replacement comp than play it safe and mount it the way the old one is mounted

  11. #11
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: Is a Potetial relay position sensitive?

    if it came with replacement comp than play it safe and mount it the way the old one is mounted
    The old compressor only had a start cap w a cmr relay. The replacement has both a start and run cap with a potential all supplied by Danfoss. No mounting bracket or instructions will have to make something.

    Ken

  12. #12
    Join Date
    Feb 2006
    Location
    ct
    Posts
    11
    Rep Power
    0

    Re: Is a Potetial relay position sensitive?

    give me some numbers Ill look it up if you havent already isntalled it or blew it up.

Similar Threads

  1. voltage drop on relay
    By Temprite in forum Electrical
    Replies: 4
    Last Post: 30-01-2006, 07:55 PM
  2. Potential Relay not staying open
    By labrosse in forum Technical Speculations
    Replies: 4
    Last Post: 05-08-2005, 08:14 PM
  3. Freezer Potential Relay not staying open
    By labrosse in forum Trouble Shooting
    Replies: 0
    Last Post: 28-10-2003, 01:53 AM
  4. Alternating Relay Circuit
    By herefishy in forum Industrial
    Replies: 3
    Last Post: 09-07-2002, 06:03 PM
  5. Drier Position
    By subzero*psia in forum Commercial
    Replies: 8
    Last Post: 23-07-2001, 10:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •