Thread: Stulz ASD 1052
-
16-04-2013, 05:14 AM #1
Stulz ASD 1052
Hi guys
does anyone know much about these units? I am currently having an issue with a comp2/hp fault.
I have bridged out the compressor overload as I thought this may have been going off. But the unit still fails. I then thought the hp wire connections were loose so I tightened the terminals. But the unit still fails. The hp switch has a manual reset button which has never activated so I am wondering why this fault keeps occurring.
I have check all wire connections and made sure everything was tight. Could it be that he pc board is faulty? I'm out of ideas.
-
16-04-2013, 08:06 AM #2
Re: Stulz ASD 1052
I've never seen Stulz. But I think you can check Input/Output in submenu of controller and take a decision.
-
16-04-2013, 09:18 AM #3
Re: Stulz ASD 1052
its been a while since i have worked on one of these units.... but about 5 years ago i was working on one in the presence of a technician from stulz themselves, and i vaguely remember him telling me that a hp fault doesnt just mean a hp fault (ie high pressure) but it can also mean a bunch of other things, like overload etc, its almost like a universal fault code.
id be seeing what other safetys it has and be checking them....
i think they have a separate lp fault so u can probably rule that out....
good luck!!
actually the more i think of it, i think they may have a high discharge temp sensor/safety, which i think he said ties in with the hp fault.... maybe its slightly short of gas?? somewhere to start anyhow....Last edited by Mick13; 16-04-2013 at 09:22 AM.
-
16-04-2013, 01:35 PM #4
Re: Stulz ASD 1052
Hi Mick, there is also a habit for Stulz and other manufacturers to wire the compressor protection modules into the HP control circuit. So if this module trips (located in the Copeland compressor terminal box) it will also show as a HP fault. Look specifically at the control voltage to, if your getting more than 10% above 24V, the compressor protection modules can fault due to high control voltage. So basically, you attend for a HP fault and the units in alarm, and yet you press the HP reset button and no 'click'. Seen this more than once on Stulz units, particularly if the site voltage is high and the Stulz control transformer has not been tapped appropriately ie 400V.
Hope this helps.
-
17-04-2013, 01:00 AM #5
-
17-04-2013, 12:11 PM #6
Re: Stulz ASD 1052
If it's a (Danfoss iirc) dual HP switch, there might be a second, pressed metal push button hidden under the front cover of the switch, top centre.
Silly question I expect, but have you made sure there's no manual on site? The only Stulz I've worked on so far had one stashed in the PABX room nearby.
-
17-04-2013, 01:45 PM #7
Re: Stulz ASD 1052
Measured the control voltage before and after the switch?
-
17-04-2013, 06:23 PM #8
Re: Stulz ASD 1052
Has it got a discharge transducer? If so it may be reading incorrect causing the HP fault. When in fault check the voltage either side of the HP switch and at the PCB. If this is ok it could be a possible faulty PCB.
-
18-04-2013, 01:58 PM #9
Re: Stulz ASD 1052
I have been told to check the 24v voltage to make sure it isn't low or too high.
the problem with checking the voltage when it fails is I am never there its always tripping at 3 in the morning or 10 at night and it might run for 4 days straight then trip. It's really intermittent.
i bridged out he hp switch today to see if it runs all night.
-
18-04-2013, 06:53 PM #10
Re: Stulz ASD 1052
do you have electric diagram for this unit?
-
22-04-2013, 05:40 AM #11
Re: Stulz ASD 1052
I wish It did. I'm going to try change the pc board and see what happens.
-
22-04-2013, 07:53 AM #12
Re: Stulz ASD 1052
Last HP fault that is not the real HP was on Daikin Chiller. Big RED button "Alarm cut off" make HP on all counters.
-
01-05-2013, 12:59 PM #13
Re: Stulz ASD 1052
I have by passed all the safety circuits and leaving the unit run for a few days and see what happens. The pc boards for these units are very expensive.
-
01-05-2013, 09:22 PM #14
-
02-05-2013, 12:51 AM #15
Re: Stulz ASD 1052
It would be a good outcome!