    Whats the prefered solenoid valve location



    Is it ok to locate a solenoid valve in the refrigerated space next to the evaporator? Such as in the case of a small unit cooler for a reach-in. What are the prefrerred locations for remote installations as well as self contained situations. Ken



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Whats the prefered solenoid valve location

    I would suggest the solenoid valve be located close to the expansion valve. With the valve close to the TXV, the amount of refrigerant pumped down is limited to the evaporator and the suction line.

    If the solenoid valve is close to the receiver, the entire liquid line is pumped out which could take longer.

    For small installations such as reach-in cabinets, I don't think the location matters.

    In either event, I would suggest the use of a waterproof solenoid coil.

    Whose valves are you using?

  3. #3
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19
    hi
    yes ,,i beleve that the pumpdown take less time with the solinoid valve be behind evaporator,,,but a disadvantage came here ,,that it is difficult to maintain the s.v. , watching its operation ,
    and with relative of this position , the sightglass that must be put after the s.v. ! how can be watched if it located neer evaporaror?
    in the small walk-in the s.v. can be located neer evap.
    but in the big once , the s.v. must be neer our hands
    thanks

  4. #4
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Whats the prefered solenoid valve location

    Whats a 's.v.'?

    Is it sight glass?

    If so the s.g. is normaly fitted to the cond unit. I dont think fitting a s.g. after a solinoid is a good idea, It will be subjected to freezing when the solinoid shuts and the cond unit pumps down.

    It may crack the glass.


    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  5. #5
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Whats the prefered solenoid valve location

    I asume SV is Solenoid valve

  6. #6
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Whats the prefered solenoid valve location

    I asume SV is Solenoid valve
    Oh yeh.. so it is, my head was getting mashed by the wife talking at the time.


    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Whats the prefered solenoid valve location

    Quote Originally Posted by US Iceman
    If the solenoid valve is close to the receiver, the entire liquid line is pumped out which could take longer.
    And if the line is long from the SV to the TEV, if you open the SV, it will knock very hard on the lines, sometimes bursting elbows.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: Whats the prefered solenoid valve location

    In either event, I would suggest the use of a waterproof solenoid coil.

    Whose valves are you using?
    I use Sporlan solenoid valves and have not had a water related problem. It can be difficult to check its operation when servicing but other than that it seems to work fine. In a remote display case, med temp, I have always put the solenoid valve just before the TEV, and in some situatons it's the perfect location. My supervisor insists that the cold will cause malfunction of the valve. Ken
    Last edited by kengineering; 02-02-2006 at 12:21 AM. Reason: Added quote to post.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Whats the prefered solenoid valve location

    My supervisor insists that the cold will cause malfunction of the valve
    I don't buy that argument Ken.

    The valves get cold every time the system goes through a pump down cycle.

    I use the Sporlan components for any small project I am involved in. During my years as a service tech I had much better results with no problems when using Sporlan products.

  10. #10
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: Whats the prefered solenoid valve location

    Thanks Iceman.

  11. #11
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Whats the prefered solenoid valve location

    My supervisor insists that the cold will cause malfunction of the valve.
    We have put SV`s in cases for years, fridges, freezers never had a problem.

    Just make sure they are water-proofed and you should have no problems.


    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  12. #12
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: Whats the prefered solenoid valve location

    Just make sure they are water-proofed and you should have no problems.
    When you say "water-proofed" what type precautions should be taken? I would think the coil is sealed so I assume you mean the electrical connections. Could you be more specific on the waterproofing. Ken

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Whats the prefered solenoid valve location

    Well, that the cable entries can widhstand a humid environment and you install the valves the correct way.
    For example the Danfoss valves: the old coils had to be fixed with a top cap with a rubber O-ring in it.
    If the valve is standing right, then you don't need tho fix this coil and you see it often installed this way.
    But water can then enter between the valve spindle and the coil and during a longer standstill in freezing conditions, it can damage the spindle.

    The coils are no made out of one piece (included the extruded top cap) and they click on the valve now so that it is always sealed.
    I heard Danfoss modified this coil due to the freezing problems.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Whats the prefered solenoid valve location

    Quote Originally Posted by Marc O'Brien
    And then the answer to the puzzle is finally revealed by Gary in the seventh post on this page:

    http://www.fridgetech.com/discussion...ges/42/131.htm

    with my comments immediately after...
    The page cannot be found
    The page you are looking for might have been removed, had its name changed, or is temporarily unavailable.
    --------------------------------------------------------------------------------

    Please try the following:

    Make sure that the Web site address displayed in the address bar of your browser is spelled and formatted correctly.
    If you reached this page by clicking a link, contact the Web site administrator to alert them that the link is incorrectly formatted.
    Click the Back button to try another link.
    HTTP Error 404 - File or directory not found.
    Internet Information Services (IIS)

    --------------------------------------------------------------------------------

    Technical Information (for support personnel)

    Go to Microsoft Product Support Services and perform a title search for the words HTTP and 404.
    Open IIS Help, which is accessible in IIS Manager (inetmgr), and search for topics titled Web Site Setup, Common Administrative Tasks, and About Custom Error Messages.
    Takes a licking, keeps on ticking.

Similar Threads

  1. tx valve bulb location
    By adam in forum Technical Speculations
    Replies: 28
    Last Post: 26-11-2009, 07:52 PM
  2. Blistering Hot Gas Solenoid Diaphragm Issue
    By dewars_aus in forum Trouble Shooting
    Replies: 7
    Last Post: 18-07-2006, 09:37 PM
  3. exp valve location
    By bernard in forum Supermarket Refrigeration
    Replies: 6
    Last Post: 18-08-2005, 10:22 AM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •