    DAIKIN multi split fault



    Hi guys can anyone help I have a Daikin multi system 4mxs80e7v3b1 with 4 cassettes one of which is not heating and cooling most of the time. The other three heat and cool perfectly and sometimes the other unit works fine but seems to be only when the others are on aswell. I pretty sure it's not low on gas as the pressures seem there or there abouts. R410a. Changed the expansion valve head for one which works buy no success I ran out of time on site tho so was hoping someone could help for the next visit??
    thanks

    lee



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: DAIKIN multi split fault

    Sensors?
    TEV body?
    Strainer?


  3. #3
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: DAIKIN multi split fault

    Pretty sure the strainers are ok as the other units work fine, valve body I'm not sure as they are hard to test esp the fact that it works intermittently and the sensors all seem fine

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: DAIKIN multi split fault

    lev on outdoor not motoring open- swapping the heads wont cure it, and if your using all 4 ports u cannot swap circuits to proove this

  5. #5
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: DAIKIN multi split fault

    I think the fact that it works sometimes is stumping me as surely if the EV was not opening it would never work??

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: DAIKIN multi split fault

    I don't know what indoor unit's you got but Daikin sometimes put strainers inside the pipes just behind the flares on the indoor units.
    Seen it in the past where moisture in the system get stuck in this mesh and creates a blockage when it freezes.

    Unlikely but something to bear in mind.


  7. #7
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: DAIKIN multi split fault

    Thanks I will look into that

  8. #8
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: DAIKIN multi split fault

    Yep...if EEV in indoor and strainer jamed you hear gurgle in cooling mode, if EEV in outdoor temp. before and after strainer different.

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: DAIKIN multi split fault

    Is the total pipework length within 75m?

    Is the troublesome cassette within 25m of the outdoor unit?

  10. #10
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: DAIKIN multi split fault

    Had the same problem last year on a 2MXS50F - ordered both expansion valve body and valve coil turned out it was just the coil in the end so 10min job.

    However had this on Daikin RK/XS splits in the past and turned out we had to replace the valve body so could be this or as Frank has said above.

  11. #11
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: DAIKIN multi split fault

    FRANK The total pipe runs are border line 75m and this unit is about 20m, why can one unit not be more than 25m??
    SLIM yes I was edging towards the EV body as I have had many Daikin units in the past with dodgy valves body and head seems common fault tbh

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: DAIKIN multi split fault

    Quote Originally Posted by leegally1983 View Post
    FRANK The total pipe runs are border line 75m and this unit is about 20m, why can one unit not be more than 25m??
    It's all about pressure drops...pipe resistance to flow etc...

    Manufacturer's make the rules, we just have to live by them...

  13. #13
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: DAIKIN multi split fault

    Quote Originally Posted by frank View Post
    It's all about pressure drops...pipe resistance to flow etc...

    Manufacturer's make the rules, we just have to live by them...
    Or not if needs arise :-)

  14. #14
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: DAIKIN multi split fault

    Managed to get back on site and have a play around with the unit again looks like its the valve body there is just nothing coming through it, thanks for your help guys

  15. #15
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: DAIKIN multi split fault

    Did you check step motor?

  16. #16
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: DAIKIN multi split fault

    step motor?? do you mean the expansion valve head/motor?

  17. #17
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: DAIKIN multi split fault

    Yes, i mean that) If you can change heads on working unit, do it) And look what happend with bad indoor unit.

  18. #18
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: DAIKIN multi split fault

    Hi Guys

    Bit of feedback, i went to site and there was a spare port so we swopped the faulty circuit to the spare one and re-commissioned it and the faulty indoor unit worked.
    We left site anyway we have had a call today saying it now has a U0 fault which means low pressure, faulty exp valve, faulty low pressure sensor or blockage.
    This seems strange as we left all units running fine and pressures were good so i am abit bewildered by this we are going back to site tomorrow to have a look any suggestions?

  19. #19
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: DAIKIN multi split fault

    Blocked strainer?? Faulty pcb?

  20. #20
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: DAIKIN multi split fault

    had it on a daikin multi split U0 error- get the hose pipe on the condenser, visibly looked clean but got a load of crap outta it, then check the charge- also which unit is designated as a master?? - outdoor dip switcha-d if u swapped port and that was a master then that wont help, im assuming u swapped the wiring over too
    Quote Originally Posted by leegally1983 View Post
    Hi Guys

    Bit of feedback, i went to site and there was a spare port so we swopped the faulty circuit to the spare one and re-commissioned it and the faulty indoor unit worked.
    We left site anyway we have had a call today saying it now has a U0 fault which means low pressure, faulty exp valve, faulty low pressure sensor or blockage.
    This seems strange as we left all units running fine and pressures were good so i am abit bewildered by this we are going back to site tomorrow to have a look any suggestions?

  21. #21
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: DAIKIN multi split fault

    when I got on site I found some bright spark had the central heating on with a rad in his office and because he was too hot instead of turning down the rad he decided to put the unit on 16 degrees cooling and then left his office door open poor unit had been running flat out all day .................. bit of training for the customer problem solved thanks for the help guys