    Lightbulb design



    Hi all,

    I have been asked to connect a Trane RAUL 190(cooling only) to a Trane AHU on a roof with about 6 metres of pipework.
    I cannot find full installation information but I know the condenser has 1"5/8, 7/8" connections and the units are matched on R407C with a 55 Kw capacity.

    My concerns are these,

    I'm not sure if I should run the pipe in the afore mentioned sizes.

    I will need to install a drier and sight glass in the liquid line, do I also need a suction drier.

    What expansion valve will I need and what orifice.

    Approximatley how much R407C should I estimate to use.

    I dont normally have to design, any help would be appreciated.



  2. #2
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: design

    holy moley...........................................

  3. #3
    Join Date
    Jan 2005
    Location
    england
    Age
    48
    Posts
    64
    Rep Power
    20

    Re: design

    dogma,

    explain

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: design

    Freezy, have at look at the Trane manual for the RUAL unit, it provides performance data for the gas you want to use... see here...
    http://www.trane.com.au/equipmentdocs/RAUL.pdf
    hope this helps.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: design

    It never harms to install a suction line filter dryer.
    The first core is made of some woven fabric, replaced after some running hours by a fine mesh filter.

    Make sure the copper lines are installed the right way.

    1 5/8 suction and 7/8 liquid.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Jan 2005
    Location
    england
    Age
    48
    Posts
    64
    Rep Power
    20

    Re: design

    Thanks peter,

    I am unsure about the 7/8" liquid line, it seems quite large for a 55 Kw evaporater. Does this mean my expansion valve should have a 7/8" inlet connection as this would probably be a power assembley valve, I cannot find a TEV with connections above 5/8". danfoss TX2's, etc have capacities opto about 150 Kw but they have 3/8" connections.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: design

    Quote Originally Posted by freezy
    Thanks peter,

    I am unsure about the 7/8" liquid line, it seems quite large for a 55 Kw evaporater. Does this mean my expansion valve should have a 7/8" inlet connection as this would probably be a power assembley valve, I cannot find a TEV with connections above 5/8". danfoss TX2's, etc have capacities opto about 150 Kw but they have 3/8" connections.
    A TX2 for 150 kW? Impossible. Something around 25 kW maxi should be better but 150 kW???Perhaps without an orifice in it

    7/8 is correct, it depends of course also on the allowable pressuredrop and speed in the lines. I take usually 10 m/s.

    You may try it with a smaller 3/8 or 1/2, it's your installation.

    You will need a TE5 with an orifice 04, just looked in the manual.

    But, I'm also a little afraid that you don't quite understand the basics. Is your boss not able to select these items and the lines? If he isn't, then he better should go back some time to school again.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. capillary tube design
    By Chris Zahrt in forum Fundamentals
    Replies: 5
    Last Post: 04-06-2009, 09:16 PM
  2. Mini liquid Chiller design
    By Sockit2me in forum Fundamentals
    Replies: 2
    Last Post: 10-02-2006, 06:38 PM
  3. R134a <-> liquid heat exchanger design
    By DaBit in forum Technical Speculations
    Replies: 19
    Last Post: 10-05-2002, 08:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •