    daiken splits difference between f3 alarm and e4



    Hi guys I am new to this forum so please dont be too harsh my background has been mostly chillers so pretty new to air con I was at a site today 4 splits 3 showing code f3 and 1 showing e4 further inspection the e4 unit short of gas but the others high discharge temp could this be down to shortage of gas or possibly one of the fans is not rejecting latent heat

    Thanks



  2. #2
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: daiken splits difference between f3 alarm and e4

    Quote Originally Posted by craigmouring View Post
    Hi guys I am new to this forum so please dont be too harsh my background has been mostly chillers so pretty new to air con I was at a site today 4 splits 3 showing code f3 and 1 showing e4 further inspection the e4 unit short of gas but the others high discharge temp could this be down to shortage of gas or possibly one of the fans is not rejecting latent heat

    Thanks
    Operate each system with gauges on. Sounds to me like a shortage of gas on all of them!

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daiken splits difference between f3 alarm and e4

    check indoor filters and outlets havent been blanked off

  4. #4
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: daiken splits difference between f3 alarm and e4

    F3 ... that the discharge pipe temperature has increased greatly above normal operation levels.
    This can be caused by a fault with the compressor if the oil return to it is poor it could start to run to hot or possibly even a shortage of refrigerant not cooling the compressor effectively.

    This could be either R3T, R3-1T, R3-2T, or R3-3T depending on the VRV model installed.
    Could also be a dodgy comp , had that before on an f3 fault , Also thermistors

  5. #5
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: daiken splits difference between f3 alarm and e4

    E4 This is stating that there has been a low pressure error on the system.
    This could have been caused by a blockage in the pipe work or a possible shortage of refrigerant. It could also be due to a fault with the low pressure sensor/switch

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: daiken splits difference between f3 alarm and e4

    Also with the E4 fault, if it is an old system with long pipe lengths you can sometimes have a slow suction pressure build up and the PCB times out the LP bypass before the pressure has risen.

    Could also be a faulty pressure switch.

    I have problems with some old kit in these slightly cooler mornings when the LP trips due, I think, to the PCB getting worn, old and bloody minded. The condenser fans are still on full chat during the start-up phase which keeps the pressures low and the LP times out, hence an E4.

    With the F3 check the pipe temperature with the unit running.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: daiken splits difference between f3 alarm and e4

    Do you know the unit model numbers?

    Where the units operating in heating or cooling mode when the errors occured?