Results 1 to 2 of 2
  1. #1
    Join Date
    Jan 2010
    Location
    Egypt
    Posts
    9
    Rep Power
    0

    matching & Balancing between Evaporator and Compressor ??



    How Can matching & Balancing between Evaporator and Compressor ?? I need know what the rule and allowance ratio between evaporator capacity and compressor capacity to matching together .( i.e if the evaporator capacity bigger than compressor capacity or lower than it to matching together without any problem ) Please details explain if you can .



  2. #2
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: matching & Balancing between Evaporator and Compressor ??

    rhi
    matching &balancing between evaporator&condensing unit depend on many factors
    1-humidity
    2-type of product
    3-outside temperature
    4-inside temperature
    selection of both must b based on calculation of room load
    if the evaporator is bigger than condensing unit&there is a limit ur humidity is bigger d.t between 6-8degrees
    if the evaporator is smaller u have less humidity&d.t 10degrees
    about matching u can do it by the good selection of txv but as i said there a limit u have to dig more &good u ask