    Condenser Replacement



    Hi, I have an old carrier r22 dustbin type unit rated at 12kw serving a dx coil mounted in a supply air duct and control is by a solenoid valve on the suction line that causes the condenser to pump down and go off on lp when temperature is achieved.
    I want to replace the condenser unit with a 407c unit to keep existing pipe and coil, do I just need to get a 12kw condenser unit and can the expansion valve be sized to this?
    Any help would be greatly appreciated thanks.



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Condenser Replacement

    Quote Originally Posted by tonyk View Post
    Hi, I have an old carrier r22 dustbin type unit rated at 12kw serving a dx coil mounted in a supply air duct and control is by a solenoid valve on the suction line that causes the condenser to pump down and go off on lp when temperature is achieved.
    I want to replace the condenser unit with a 407c unit to keep existing pipe and coil, do I just need to get a 12kw condenser unit and can the expansion valve be sized to this?
    Any help would be greatly appreciated thanks.
    you can use the same expansion valve.it has very similar properties to r22.you should flush out the circuit and charge POE oil.
    moideen-dubai

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Condenser Replacement

    407f will be a better choice, the new condensing unit should be the same size, When you state that you want condensing unit for 407c or f, it will come with POE oil, Place the SV on the liquid line before the TXV, clean the pipes with any certified cleaning agent to remove mineral oil left overs.

    Check the SV for leaks after you run the new system, oil changing can affect the rubber seal.

  4. #4
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Condenser Replacement

    Quote Originally Posted by chemi-cool View Post
    407f will be a better choice, the new condensing unit should be the same size, When you state that you want condensing unit for 407c or f, it will come with POE oil, Place the SV on the liquid line before the TXV, clean the pipes with any certified cleaning agent to remove mineral oil left overs.

    Check the SV for leaks after you run the new system, oil changing can affect the rubber seal.
    The best agent for removing the existing MO is R22, used in a closed circuit. When you properly clean the whole rest of the installation, evaporators i.e., you will achieve also a better performance.
    Agree with Chemi Cool, the mixture of POE+HFC will attack the seals elastomerers and create leakages, so it would advisable to switch the seals to neoprene ones.
    Read case study of a R22 conversion to R407C here: www.fri3oilsystem.com/retroficase.zip

    Regards,

    Nando.

  5. #5
    Join Date
    May 2008
    Location
    CROYDON
    Age
    61
    Posts
    13
    Rep Power
    0

    Re: Condenser Replacement

    Thanks guys advice taken and understood.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Condenser Replacement

    all aluminium coil on a carrier dustbin- scrap yards love em!