Thread: Daikin rooftop defrost problems
-
27-11-2012, 10:53 PM #1
Daikin rooftop defrost problems
I have five Daikin rooftop model UATYP 560AY1 with same problem :
in winter , in HEATING mode , defrost program is too short and ice cover the condensers .
( all the rooftops are mounted in same conditions )
If i change sensor positions on condensor , the defrosting period is the same .
I want to increase the defrost time ( if is possible...) , but i don't have technical manual for PCB .
Please help me with some informations ....
Thanks in advance
-
27-11-2012, 11:20 PM #2
Re: Daikin rooftop defrost problems
you need to comfirm the correct gas charge- or compare running pressures with the 4 normal units,also clean condenser coils can affect systems
-
28-11-2012, 08:22 AM #3
Re: Daikin rooftop defrost problems
Daikin technicians checked all parameters, all is normal , but did not have a technical solution. When increase the humidity at temperatures below 5 degrees C, ice accumulates progressively on condenser. PCB has a fixed duration of deicing, which reduces with the temperature measured by the sensor.
-
28-11-2012, 07:05 PM #4
Re: Daikin rooftop defrost problems
You should be able to change the defrost frequency, i think it's a jumper wire? Alternatively if all else is ok, fit a timeclock, knock out indoor fan and connect to 4 way valve.
alMostly found in the southern part of this green and pleasant land.
-
28-11-2012, 10:56 PM #5
Re: Daikin rooftop defrost problems
dip switch 1-8 doesn't allow for changing defrost duration, is there an economiser on the unit or a manual fresh air damper on it?