    Daikin rooftop defrost problems



    I have five Daikin rooftop model UATYP 560AY1 with same problem :
    in winter , in HEATING mode , defrost program is too short and ice cover the condensers .
    ( all the rooftops are mounted in same conditions )
    If i change sensor positions on condensor , the defrosting period is the same .
    I want to increase the defrost time ( if is possible...) , but i don't have technical manual for PCB .
    Please help me with some informations ....

    Thanks in advance



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin rooftop defrost problems

    you need to comfirm the correct gas charge- or compare running pressures with the 4 normal units,also clean condenser coils can affect systems

  3. #3
    Join Date
    Oct 2005
    Location
    Romania
    Posts
    44
    Rep Power
    0

    Re: Daikin rooftop defrost problems

    Daikin technicians checked all parameters, all is normal , but did not have a technical solution. When increase the humidity at temperatures below 5 degrees C, ice accumulates progressively on condenser. PCB has a fixed duration of deicing, which reduces with the temperature measured by the sensor.

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Daikin rooftop defrost problems

    You should be able to change the defrost frequency, i think it's a jumper wire? Alternatively if all else is ok, fit a timeclock, knock out indoor fan and connect to 4 way valve.

    al
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin rooftop defrost problems

    dip switch 1-8 doesn't allow for changing defrost duration, is there an economiser on the unit or a manual fresh air damper on it?