    Formula to size Refer unit for Beverage cooler



    Hello All, I need to size a new 404a condensing unit for a reach-in (front loading)beverage cooler. Specs: 12 doors-30"W x 24"D x 60H". Its in a small store, over along the wall, so its approx. 30' in length. Of course its medium temp. I'm replacing a Russell unit that had a 6hp copeland discus- grounded out(I wonder Why!?)Owner said it was always icing-up. What do you think? I think a 1 1/2 or 2 horsepower unit. What else do I need to know? Please advise.
    Last edited by mccoolair@yahoo; 10-01-2006 at 11:48 PM.



  2. #2
    Join Date
    Jan 2006
    Location
    Fort Worth, Texas
    Age
    74
    Posts
    19
    Rep Power
    0

    Question Re: Formula to size Refer unit for Beverage cooler

    Hello All, I need help sizing a Refrig. Condensing Unit:
    Medium Temp- 35F
    R404a
    Cabinet Style: Bev. Cooler- front loading
    12 doors- 30"wide each
    Approx.total length- 30'
    Depth-24", Height- 60"
    Area- 300 cubic ft.

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Formula to size Refer unit for Beverage cooler

    Figure 1000 to 1200 Btu/door at 20 deg F. A one hp would be marginal depending on traffic. I would size a 2 hp compressor.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Formula to size Refer unit for Beverage cooler

    Quote Originally Posted by mccoolair@yahoo
    ..... I'm replacing a Russell unit that had a 6hp copeland discus- grounded out?....I think a 1 1/2 or 2 horsepower unit. What else do I need to know?
    Why it was icing up? You have yourself the answer for this problem.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jan 2006
    Location
    United Kingdom
    Posts
    8
    Rep Power
    0

    Re: Formula to size Refer unit for Beverage cooler

    i'm confused!
    what's icing up?... the evaporator? or the suction to the compressor? and you need a separate condensing unit? for what reason?

  6. #6
    Join Date
    Sep 2005
    Location
    Atlanta Georgia USA
    Age
    69
    Posts
    80
    Rep Power
    19

    Re: Formula to size Refer unit for Beverage cooler

    Like Peter said you have a problem. The freeze-ups probably caused flood-back that caused the grounded compressor.

    Medium temp closed door case need about 350 to 550 btu/ft at +20*F evap temp, that will vary greatly by who manufactured the cases, you need to verify the BTUH requirements.

    I don't know your store or ambient conditions but that size looks about right, there are many variables though.

    Steve Wright CM
    Last edited by Steve Wright; 15-01-2006 at 01:45 AM. Reason: clearify

  7. #7
    vipul's Avatar
    vipul Guest

    Re: Formula to size Refer unit for Beverage cooler

    Please confirm the following:

    1. Is this Reach in cooler in an air conditioned area? Or else, please let me know the temperature of the surrounding air.

    2. What is the ambient temperature for the condensing unit?

    3. What is the distance between the Walkin and the location of the condensing unit?

    4. Are the bottels being loaded in the cooler, pre cooled or at normal temperature?

    Look forward to your reply and then I can do the heat load for you.

    Regards,

    Vipul Chandra
    Dubai


    Quote Originally Posted by mccoolair@yahoo
    Hello All, I need to size a new 404a condensing unit for a reach-in (front loading)beverage cooler. Specs: 12 doors-30"W x 24"D x 60H". Its in a small store, over along the wall, so its approx. 30' in length. Of course its medium temp. I'm replacing a Russell unit that had a 6hp copeland discus- grounded out(I wonder Why!?)Owner said it was always icing-up. What do you think? I think a 1 1/2 or 2 horsepower unit. What else do I need to know? Please advise.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Formula to size Refer unit for Beverage cooler

    And the wall thickness?

    How many times will the doors open? If it's like in a highway shop, every minute open the door, looking a minute what they should drink with the doors wide open, and then pick the bottle and shut the door not properly afterwards.

    Initially there was a 6 HP !!
    Now replaced with a 1 1/2 HP.

    What size of standard evaparator fits in this closet?

    Distance between room and compressor...why you need this?

    A rough estimate after converting the " ' " ( ' " ! § ( ...1500 W.
    But such an evaporator can't be installed in a room of only 65 cm (héhé) deep. So you will need to install at least 2 evaporators or foresee a false ceiling with a tailormade evaporator in it, ventilated by a centrifugal.

    Or even better a 13th section with a vertical tailor made evaporator in it and a turbine and a false ceiling.

    Or use a part of the 12th door to in stall one.

    Is there place on the ceiling.

    Choose also one with a high DT, conservation is not an issue here.

    We've done with the company I worked for - together with BESC5240 - some for Totalfina along the highway Brussels-Ostend: glassdoors, charged from the cold room behind. One side of the cold room were in fact the glassdoors for the clients.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Jan 2006
    Location
    Fort Worth, Texas
    Age
    74
    Posts
    19
    Rep Power
    0

    Re: Formula to size Refer unit for Beverage cooler

    Peter, I found your post regarding" sizing Refer unit for a beverage cooler" informative. The ballgame has completely changed since then; the store is in a very low income area so consequently, money is the main issue. A liquidating compny, of the same ethnic background as the store owner (their buddies),is to provide a Copeland 3hp compressor to replace the 6hp, in otherwards putting a 3hp compressor in a 72,000 btu condensing unit. The 3hp comp. is designed for R-502,R-12, or R-22 refrigerants. These people deal in used commercial refrigeration systems, for supermarkets, convenience stores and comm. kitchen equipment. I will be changing the TXV for R-22 application. To answer some of the questions you had, The distance between the appliance and condenser is approx. 20 ft.; the beverages arrive pre-cooled; thickness of the cabinet- don't know; Indoor ambient ranges from 70-80, and outdoor temp.- winter= 25-80 degreesF; summer= 70-105 degrees F. Its in Dallas, TX. I apologize for what appears to be a "jerry-rigged" job. I'm just trying to do the best I can with what their giving me to work with.

  10. #10
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: Formula to size Refer unit for Beverage cooler

    Watch if something goes wrong it don't come back and bite you on the bum. Record everything, I'm presuming you have a boss, log it all and include your notes and corespondance with your concerns when doing "jerry-rigged" jobs. You don't want a nice big fine from your local gov or EPA.