    eliwell 961
    Can somebody please help me. first time i am using this controller and it keeps giving me a reading of 100 degrees celcius, i put my lighter against the sensor and the reading goes down i take it off and it goes back up. does anybody have any idea what is going on?
    Feb 2009
    telford
    2,090
    33
    Re: eliwell 961
    try another probe?when you disconnect it switch it on and see if comes up with the probe fault have you extended the probe with extra cable if so ensure the connections are good its good practice to solder them
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2007
    Hampshire
    438
    32
    Re: eliwell 961
    You need to change probe setting.
    1 = NPC or 0 = PTC in configuration menu CNF (H00)
    Nov 2012
    uk
    3
    Re: eliwell 961
    it is a new controller (new shape). it doesnt have the H00 and it automatically recognises the probe NPC or PTC
    Nov 2012
    uk
    3
    Re: eliwell 961
    and i have used 3 different sensors and bought a new controller in case it was faulty but got the same problem
    hookster's Avatar
    Apr 2007
    Hampshire
    438
    32
    Re: eliwell 961
    Has it got a heating option?
    hookster's Avatar
    Apr 2007
    Hampshire
    438
    32
    Re: eliwell 961
    You say new shape? So I assume ID961 Plus
    As per old models CNF function H00 for probes is still in menu. I think you need to check manual or download it.
    http://www.eliwell.it/product.aspx?i...&LangType=2057
    Somerset
    69
    4,706
    Re: eliwell 961
    Hi Nallsa.
    Yours is a strange one!
    Basically as stated above all the literature for the various versions of the 961 state the either form of probe is used subject to selection within the software.
    However the below text is direct from a brochure, extracted from the elewell website.
    Dimensions: front panel 74x32mm, depth 59mm
    Mounting: panel (71x29mm hole)
    Power supply: 230V~ ±10% 50/60Hz
    Power consumption: 4.5W max
    Analogue inputs: 1 NTC (EWPlus 902/961) or
    2 NTC (EWPlus 971/974)
    Digital inputs: 1 digital voltage free input
    Digital outputs:
    EWPlus 902: 1 SPDT ½Hp 8(4)A 250V~
    EWPlus 961: 1 SPST 2Hp 12(12)A 250V~
    EWPlus 971: 1 SPDT ½Hp 8(4)A 250V~
    EWPlus 974:
    1 Front panel: IP65
    As you can see it refers to a NTC probe only?
    Maybe there is indeed a version that does not offer a choice in probe?
    Particularly as you mention no H00 setting !
    Cheers Grizzly
    I would of posted the whole brochure only mediafire is a nightmare at present.
    Anyone got any alternative sites to recommend?
    Sep 2003
    ISRAEL
    72
    4,248
    Re: eliwell 961
    Once you set the new probe, you have to switch it off and then on
    Oct 2007
    manchester
    5,639
    45
    Re: eliwell 961
    you need to access level 2 via the password
    Passwords “PA1” and “PA2” allow level 1
    and level 2 parameters to be accessed. In
    the standard configuration passwords are
    not present. To enable them (value 0)
    and assign them the desired value, access
    the Programming menu in the “diS” folder.
    If passwords are enabled, they will be
    requested:
    - PA1 when entering the Programming
    menu (see the “Programming Menu“ section);
    - PA2 in the “Cnf” folder containing level
    ho CONFIGURATION (folder with “CnF” label)
    For selection of probe type, PTC or NTC.