    Fault on mitso split system



    6month old unit
    The air con is coming up with a Fault flashing 7 times.
    In the manual it says Problems could be .

    Refrigerant is insufficient. = Refrigerant is leaking

    Heat exchanger sensor 1 error = Broken heat exchanger sensor 1 wire, poor connector connection .

    It doesnt seem to have a leak because i checked outdoor flares with bubbles. and has suction pressure at 850kpa with near 40c ambient .

    i was there for 2 hours and turned unit of and on 5 times. couldnt see fault but customer has rung up again and said its doing same thing.

    Would moisture in the system make this fault come up . but then the suction would be lower.

    Could it be faulty inner connection wires ?

    What heat exchanger should i look for sensor . out door or indoor ?



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Fault on mitso split system

    Evap coil sensor.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Nov 2012
    Location
    Australia
    Posts
    6
    Rep Power
    0

    Re: Fault on mitso split system

    indoor sensor could be faulty like stufus said cause that how it senses if there is a gas shortage if the gas is fine then the sensor is faulty giving wrong reading