Fault on mitso split system
6month old unit
The air con is coming up with a Fault flashing 7 times.
In the manual it says Problems could be .
Refrigerant is insufficient. = Refrigerant is leaking
Heat exchanger sensor 1 error = Broken heat exchanger sensor 1 wire, poor connector connection .
It doesnt seem to have a leak because i checked outdoor flares with bubbles. and has suction pressure at 850kpa with near 40c ambient .
i was there for 2 hours and turned unit of and on 5 times. couldnt see fault but customer has rung up again and said its doing same thing.
Would moisture in the system make this fault come up . but then the suction would be lower.
Could it be faulty inner connection wires ?
What heat exchanger should i look for sensor . out door or indoor ?
-
09-11-2012, 11:17 AM #2
Re: Fault on mitso split system
Evap coil sensor.
Cheers
StuTool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
16-11-2012, 04:45 AM #3
Re: Fault on mitso split system
indoor sensor could be faulty like stufus said cause that how it senses if there is a gas shortage if the gas is fine then the sensor is faulty giving wrong reading