  1. #1
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    3 phase compressor contactor failures



    What causes compressor contractor failure more than once.

    We've inherited a few old Daikin units ERC5EB and when we arrived on site we found the 3 phase compressors down to earth on both units and the compressor contactors on both units only letting through 2 of the 3 phases which has most probably caused the compressor failure.

    However the contactors have been in 2 weeks and they have failed again causing only 2 phases to be supplied to the compressors rater than the 3.

    The guy on site thinks these contactors have been changed several times in the past but what can be causing them to fail so often.

    I've checked all the obvious things electrically;

    The supply voltage and neutral has been checked (by our electrician) and proved to be ok.*
    The contactors are fitted with overloads.
    The contactors are the correct ones and the coil is the correct voltage.
    All terminals are tight.
    The compressors are brand new and so are not at fault (acid test was carried out on old ones)
    The compressors both pull around 9amps per phase with the overload set at 15amps.

    This ones a head scratcher for sure.


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: 3 phase compressor contactor failures

    A chattering pressure switch or similar in the feed to the coil will cause the contractor to pull In and drop out rapidly resulting in burnt contacts, if this is the case a time delay in the feed my help though it won't fix the original problem.

    im sure others will know of a more daikin specific problem that could be the cause also.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: 3 phase compressor contactor failures

    Hi Monkey,
    I originally thought this may be the cause but whenever I'm on site and with the units in question the feeds to the coils are constant and never drop or lose the signal.
    The refrigeration side is okay as well as both pressure switches.

    It may well be worthwhile to fit a start limit timer for say no more than 12 start per hour.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: 3 phase compressor contactor failures

    Hi Marc

    What is protecting the mains supply to the unit. Is it fuses or MCB? I would suspect it's fuses, as a large imbalance like 2 phasing should take out an MCB.

    I've only got details for the old ERC5 C series which shows the compressor contactor circuit fed from the indoor unit on wire terminal 5 which goes through the overload (95 - 96) and a delay on timer K2T (3 minutes)

    Is the current draw equal on all 3 phases?

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: 3 phase compressor contactor failures

    When you say "contactor failed", do you mean main contacts burnt? coil burnt?
    What is the amp peak start?
    What is the run amp draw?
    What is the contactor amp rating?
    What is the contactor make?

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: 3 phase compressor contactor failures

    A remote location can cause issues, as due to the distance from the grid, which we get a lot down here in the s.west.
    Can play havoc with the incoming voltages. Which in turn will cause all sorts problem. If this is related to just one set of kit then I think the others have it sussed.
    Grizzly

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 3 phase compressor contactor failures

    stick a 3 phase controller on it which detects 3 ph and will open circuit ur comms to the contactor- at least this will react quicker than the overload and prevent 2 phasing

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: 3 phase compressor contactor failures

    If its got a seperate delay timer (as opposed to built into circuit board) then i'd change it, have had these go bad and case contactor chattering.
    Mostly found in Oxfordshire, UK :)

  9. #9
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: 3 phase compressor contactor failures

    Install monkey`s got the right idea a phase failure relay drop the compressor out before any damage occurs. Also try a low voltage trip relay, if it trips on that you know you`ve got voltage supply problems.

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: 3 phase compressor contactor failures

    Overloads should trip if it loses a phase if they are set correctly, check they are not set to auto reset.

    As said above though a phase failure doodad would be extra insurance.
    Mostly found in Oxfordshire, UK :)

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 3 phase compressor contactor failures

    overloads would trip, but not instantly- thus by fitting the moniter


    3 wire 3phase under voltage relay,500Vac





    Enlarge
    Image representative of range only







    Technical Reference


    • UL/CUL E111187
    • M3PR Phase Sequence / Failure & Under Voltage Relay
    • Statement of conformity
      RS Components

      Statement of conformity




      RS Stock No. 342-944
      Description 3 wire 3phase under voltage relay,500Vac
      Manufacturer/Brand: Broyce Control
      Mfr Part No. M3PR 300-500VAC






      Contact Configuration NO/NC
      Electrical Phase Three
      Height 89mm
      Length 59mm
      Monitoring Application Phase, Voltage
      Phase Sensitivity Phase Loss, Phase Sequence
      Supply Voltage 300 → 500 V ac
      Time Delay 1 s
      Voltage Sensing Range 300 → 500 V ac
      Voltage Sensitivity Undervoltage
      Width 35mm













    Three-Phase Sequence/Failure & Under Voltage Relay

    Detects under-voltage condition
    Detects phase loss (and neutral loss on 4-wire)
    Detects incorrect phase sequence
    Adjustable trip level
    Monitors own supply
    DIN rail or surface mount



    Phase Sequence/Failure Relays

    Monitoring of 3 phase supplies





    Quote Originally Posted by monkey spanners View Post
    Overloads should trip if it loses a phase if they are set correctly, check they are not set to auto reset.

    As said above though a phase failure doodad would be extra insurance.

  12. #12
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28
    Guys I'm away from home and I'm having issues replying to this thread and have been having since Friday. The site lets me log in but won't let me reply, it just times out.
    I'm back home tomorrow and so will reply to all the comments made, thanks for all the replies.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  13. #13
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: 3 phase compressor contactor failures

    Had similar problem with failing contactors, ended up being induced voltages screwing up contactor coils releasing quickly, fitted snubber resistors across contactor coil terminals, no further problems.

  14. #14
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: 3 phase compressor contactor failures

    Contactor leg open circuits. Same phase as last time?
    If so, see if your control circuit is fed off that phase.
    Measure your full load amps and corresponding supply voltage. Your overload should have tripped before the burn-out happened.
    If the contactor is too closely rated to the running amps of the compressor, any leg is likely to burn first.

    BTW, Magoo. should your comment read " contactor coil not ​releasing quickly?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  15. #15
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: 3 phase compressor contactor failures

    Quote Originally Posted by frank View Post
    Hi Marc

    What is protecting the mains supply to the unit. Is it fuses or MCB? I would suspect it's fuses, as a large imbalance like 2 phasing should take out an MCB.

    I've only got details for the old ERC5 C series which shows the compressor contactor circuit fed from the indoor unit on wire terminal 5 which goes through the overload (95 - 96) and a delay on timer K2T (3 minutes)

    Is the current draw equal on all 3 phases?
    Hi Frank, the unit in question is an ERC8 C not an ERC5...sorry, meaning there is no delay on timer.
    It has MCBs protecting the mains supply rather than fuses and the current draw is equal on all phases.

    Quote Originally Posted by chemi-cool View Post
    When you say "contactor failed", do you mean main contacts burnt? coil burnt?
    What is the amp peak start?
    What is the run amp draw?
    What is the contactor amp rating?
    What is the contactor make?
    Hi Chemi, when I say contactors failed I meant 1 of the main contacts were burnt out of the 3.
    The overload is set to 15a and the run amp is around 9amps and balanced.

    The contactors is a Siemens type although I don't have the model at the min.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  16. #16
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: 3 phase compressor contactor failures

    Quote Originally Posted by install monkey View Post
    stick a 3 phase controller on it which detects 3 ph and will open circuit ur comms to the contactor- at least this will react quicker than the overload and prevent 2 phasing
    Yeah that's another idea install, good suggestion, I'll look into this.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  17. #17
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: 3 phase compressor contactor failures

    Quote Originally Posted by Magoo View Post
    Had similar problem with failing contactors, ended up being induced voltages screwing up contactor coils releasing quickly, fitted snubber resistors across contactor coil terminals, no further problems.
    How did you figure out that it was induced voltage that was causing the issue Magoo?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  18. #18
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: 3 phase compressor contactor failures

    Quote Originally Posted by mikeref View Post
    Contactor leg open circuits. Same phase as last time?
    If so, see if your control circuit is fed off that phase.
    Measure your full load amps and corresponding supply voltage. Your overload should have tripped before the burn-out happened.
    If the contactor is too closely rated to the running amps of the compressor, any leg is likely to burn first.

    BTW, Magoo. should your comment read " contactor coil not ​releasing quickly?
    Hi Mike,
    I think it may be the same phase as last time although I can't be certain.
    The control circuit doesn't come from a live in the condensing unit but a switched live from the time clock in the HVAC panel.
    Full load amps were 9.5a and supply voltage 235.

    The overload never trips but instead the main MCB in the fuse board trips.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  19. #19
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: 3 phase compressor contactor failures

    Hi Marc

    just a thought, what else is drawing power off that same phase

    looked at a condensing unit the other day, that had a new contactor fitted recently and went down again

    was at a petrol filling station and there was a fault with the single phase petrol price sign

    that was some how fed from the same L1 as the condensing unit

    R's chillerman
    If the World did not Suck, We would all fall off !

  20. #20
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 3 phase compressor contactor failures

    try higher rated contactors- inertia on start up could be causing contacts to wear- were the previous contactors the correct rating?
    used to go to 3 ph fujitsus aoy36's where muppets had fitted danfoss cI9 contactors- used to last about 6 months until starting current used to weld the contacts or frazzle em

  21. #21
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: 3 phase compressor contactor failures

    Basically sat there and watch system stop, the contactor spluttered. So when stopped checked contactor coil terminals with an electronic multimeter, read 80 odd volts, no potential with a dusspol check. Fitted bleed resistors to drain induced voltage. Came across the problem decades ago with early genertion Allen Bradley PLCs, all outputs to contactors etc., had to have bleed resistors at contactors.

  22. #22
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: 3 phase compressor contactor failures

    One more thing that comes to my mind after replacing compressor overload relay today.
    make sure that the screws which hold the wires, will be tight, very tight, as tight as you can.

    Copper wires behave like water pipes, when the amps are high, you can see them move and try to be straight, the same with high pressure in water pipes.