    daikin RZQ100



    Hi
    I have changed the pcb and inverter in Daikin RZQ100
    and I with new pcb in my remote control U4 error comes up. in out door pcb green HAP light bilking and red is off. and on inverter board green light is on
    Dose any body know about this problem??
    I am So please if you can give your idea..



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: daikin RZQ100

    some pcbs need to have the dip switches set befor instaling as the same board can fit several units 4.2 Malfunction of Transmission between Indoor and Outdoor Unit (
    U4 or UF)
    Error code
    U4 or UF
    Error generation
    The error is generated when the microprocessor detects that the transmission between the indoor and
    the outdoor unit is not normal over a certain amount of time.
    Causes
    The possible causes are:
    ��
    Wiring indoor-outdoor transmission wire is incorrect
    ��
    Malfunctioning indoor unit PCB
    ��
    Malfunctioning outdoor unit PCB
    ��
    Outside cause (noise...).
    Troubleshooting 1
    Diagnosis of incorrect or broken/disconnected wiring. If the LEDs on the indoor unit PC board are off,
    it indicates that the transmission wiring between indoor and outdoor units may be incorrect or
    broken/disconnected.
    Caution
    Be sure to turn off power switch before connect or disconnect connector, or parts damage may be
    occurred.
    Does
    outdoor unit
    microcomputer
    normal H1P
    flash?
    Is
    indoor-outdoor
    transmission wire
    connected
    correctly?
    Is H1P flashing?
    NO YES
    NO
    NO
    NO
    NO (ON or OFF)
    NO (OFF)
    YES
    YES
    YES
    Is HAP flashing?
    Is HBP flashing?
    To outdoor unit
    (next page)
    Is H2P on?
    Check of
    indoor unit
    microcomputer
    normal
    HAP
    Check of
    indoor unit
    transmission
    malfunction
    HBP
    YES
    YES
    Turn the power supply off
    once and then back on.
    Failure of indoor unit PCB or
    malfunction of power supply
    system.
    Resets normally.
    Could be outside
    cause (noise...).
    Failure of indoor unit PCB.
    Wire correctly.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: daikin RZQ100

    What was the original problem?

    Did you fit the capacity plug to the new PCB?


  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: daikin RZQ100

    Not the same model, I was working on an old K Series but after repowering the outdoor the U4 code keep showing until the system had 'rebooted' itself.

    Have you run a wiring check on the PCB and allowed the unit to self-test?