Results 1 to 50 of 103
Threaded View
-
24-09-2012, 06:52 AM #11
Re: COP and Superheat - does is it help?
Mad - The whole idea to set the dT to 1C is make sure excessive SH cannot be added as seems to be the case in Coolpack.
I do not know what the other programs predict but as DesA is in charge of the comparisons we shall see.
Your idea of a 50C liquid to be cooled in a counterflow exchanger is a bit outside the realm of the discussion at the moment but may be relavanrt later. The same rules will apply when this is analysed I suppose but is it realistic.
Just want to look at stuff you can but of the shelf.