    LG Inverter AC problems



    Hey guys,

    I have a LG Reverse Cycle Inverter airconditioner (r410) thats having some problems that i cant identify.

    When in heating mode the pressure at the suction service valve is reading around the 5000kpa mark but when in cooling mode i only get a reading of around 200kpa and the liquid and suction line ices up. Could this be some sort of blockage in the system.

    Where would you recommend i start looking for the problem?

    Cheers, Daniel



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: LG Inverter AC problems

    Is the indoor fan running?
    Filters clean?
    Indoor coil clean?



    .

  3. #3
    Join Date
    Aug 2012
    Location
    Townsville
    Posts
    15
    Rep Power
    0

    Re: LG Inverter AC problems

    No nothing is runnings. No indoor or outdoor. Unit is brand new first time it has been switched on.

  4. #4
    Join Date
    Aug 2012
    Location
    Townsville
    Posts
    15
    Rep Power
    0

    Re: LG Inverter AC problems

    Nevermind that last one. Was thinking of a different unit. But yes, the outdoor and indoor fan are running. Unit has been installed for a week so no dirty coil or filters

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: LG Inverter AC problems

    check the gas charge-weigh it out,also check the service valves are fully open too

  6. #6
    Join Date
    Aug 2012
    Location
    Townsville
    Posts
    15
    Rep Power
    0

    Re: LG Inverter AC problems

    Service valves are fully open. i havent weighed out gas charge but it is a brand new unit and the pipe run is within the maximum length before adding extra charge. If its short of gas it wouldnt be reaching 5000kpa when heating would it?

    Thats why im thinking blockage somewhere. In cooling it is pumping down causing the lower pressure but in heating the pressure rises as it is reversed if that makes sense>?

  7. #7
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: LG Inverter AC problems

    was ofn used whed brazing pipes if not pos blocked filter.was all the ofn removed after pressure test have you checked the refrigerant with pt chart

  8. #8
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: LG Inverter AC problems

    have you checked the expansion devise is opening if not this will give you high hp in heating and low pressure in cooling

  9. #9
    Join Date
    Jun 2011
    Location
    Australia
    Posts
    47
    Rep Power
    0

    Re: LG Inverter AC problems

    Electronic expansion Valve is where I would be looking.

  10. #10
    Join Date
    Aug 2012
    Location
    Townsville
    Posts
    15
    Rep Power
    0

    Re: LG Inverter AC problems

    How wOuld I test the expansion valve to see if it was faulty?

  11. #11
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: LG Inverter AC problems

    If there are yet other units check whether the pipes are not mixed up.

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: LG Inverter AC problems

    I would confirm the charge to rule it out as a possible cause. A frosting liquid line (after TEV/capillary on A/C) is usually a sign of SOG.

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: LG Inverter AC problems

    2 bar suction in cooling and 50 bar in heating mode,kinked pipe? or not vacced or debris in pipework

  14. #14
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: LG Inverter AC problems

    Quote Originally Posted by install monkey View Post
    2 bar suction in cooling and 50 bar in heating mode,kinky boots?
    http://www.youtube.com/watch?v=bxKBnS8GKSM
    Mostly found in Oxfordshire, UK :)

  15. #15
    Join Date
    Jun 2011
    Location
    Australia
    Posts
    47
    Rep Power
    0

    Re: LG Inverter AC problems

    Quote Originally Posted by dan_4818 View Post
    How wOuld I test the expansion valve to see if it was faulty?
    Well I had this problem once on a Mitsubishi I got hold of the service manual which had the ohm values of the EEV

    And I don't have a manual for this LG ac, so not sure what the set up is.
    Last edited by AGSelec; 17-08-2012 at 06:35 AM.

  16. #16
    Join Date
    Sep 2008
    Location
    Letsby Avenue
    Posts
    359
    Rep Power
    17

    Re: LG Inverter AC problems

    www.mylg.co.uk might help
    “Life is like riding a bicycle. To keep your balance you must keep moving” Einstein

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: LG Inverter AC problems

    I would say that Install Monkey is on right track!

    I would pump down unit and inspect pipes and indoor unit with OFN for pressure drop.

  18. #18
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: LG Inverter AC problems

    hope this helps

  19. #19
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: LG Inverter AC problems

    did you find the problem

  20. #20
    Join Date
    Apr 2010
    Location
    australia
    Age
    45
    Posts
    78
    Rep Power
    15

    Re: LG Inverter AC problems

    hp pressure to high, blocked, kinked pipe or not vac correctly. Sometimes the gauge line depressor dose not depress the schrader valve and you only vac out your gauge line. dont laugh see it done. check pipe work, blow nitro threw lines, vac and weigh in correct charge, if fails still. call out warranty agent.