    Oil carry over
    Gentlemen, A newly commissioned refrigeration plant , 10 nos HOWDEN screw compressors, 6 of them high stage 4 of them low stage cascade system, motor capaciy 630 kw HS and 200 kw LS, While compressor operating full capacity of HS compressor (above 70%) OIL carry over from oil seperator... one ltr per a minute..
    Refregerant R22
    Please advice, appreciate it
    Jul 2006
    74
    865
    26
    Re: Oil carry over
    Is just one of them doing it, or all? High or low stage?
    Is the plant operating within its design parameters?
    If it started immediately I would think the oil separator filters might not been installed properly.
    Auckland
    74
    3,357
    37
    Re: Oil carry over
    Possible HS compressors are over injecting oil, HS suction oversaturated and combined slide load rate too fast. And as NH3LVR suggested filters missing in separator.
    Aug 2012
    Dubai
    3
    Re: Oil carry over
    Hi, NH3LVR, THANKS FOR YOUR COMMENTS, All HS are loosing oil very fast , one ltr /Hr. and while running 50% load oil not loosing. coalescers filter seems good , if it is damaged or not installed properly, it may happened even 50% running .
    Compressor Howden WRVI 255/193.
    Pla advise,
    Thanks,
    Joseph PUTEN
    Sep 2008
    Canada
    811
    Re: Oil carry over
    What are the suction, intermediate and discharge pressures?
    Sep 2008
    Canada
    811
    Re: Oil carry over
    Try to lower intermediate pressure. Go to 2.5 bar and then to 2.0 bar. Monitor operation and let us know how it goes. Your oil separators might be under sized. Lowering intermediate pressure will reduce mass flow and might improve oil carry over. Did you talk to Howden?
    Aug 2012
    Dubai
    3
    Re: Oil carry over
    Hello Sir, Thanks for your comments, But if pressure drops up to 2.0 bar , intermediate temp wil be 14.5 deg C,
    That wil be effected of secondary refrigerant temp (Glyco)
    your comments will be validated
    Thanks,
    Joseph PUTEN
    3,362
    Re: Oil carry over
    Lync,
    For machines this size on R22 would expect at least 4 to 6 coalescers 225 dia x 1000mm.
    What do you have & what does contractor/supplier have to say?
    Do you know sealing design on end of filter ie "0" ring on ID or on end of filter?
    Auckland
    74
    3,357
    37
    Re: Oil carry over
    I beleive that the HS compressors are loading too fast, above 50% slide, the volumetric change and swept volume change is huge and separator velocities are huge, slow and easy load rates, system driven not load demand driven.
    Feb 2010
    new zealand
    42
    67
    15
    Re: Oil carry over
    I agree with ranger what coalescors are installed, also how are you measuring your 1L/Hr ? what is the discharge pressure and plant room temp? also why on earth is the system this size on R22? locate the designer and give him a kick from me.
    Aug 2007
    Adelaide Australia
    70
    562
    Re: Oil carry over
    Hi Lync
    Do the HS compressors have economiser lines fitted and if so do they have check valves installed?
    Paul
    Jan 2006
    Croatia
    68
    2,261
    31
    Re: Oil carry over
    Hi, all ...
    Quote Originally Posted by Nh34life View Post
    ... a big kick from me too
    what is the reason .... probably, those units are custom made, quite cheap, without proper coalescer elements both in size and quality, installed maybe, without O-rings and not tightened, for sure undersized oil separators, because until 70% capacity without oil carryover .... what about oil recovery line installed and open or not? ... it is not easy to guess what went wrong .... let's wait for OP to put some more light on this ...
    Best regards, Josip
    Sep 2004
    Germany
    80
    4
    Re: Oil carry over
    First, how come that a system like this running with R22?
    Second, what kind of oil separator do we talk about?
    Third, probably the oil separator is calculated wrong and is to small for your system.
    You have to send me all technical information and a system drawing before it possible to give you an good advice.
    hortenllc@live.com
    Jun 2008
    Finland
    45
    34
    Re: Oil carry over
    Is there solenoid valves in oil injection lines?
    I had problem once with bitzer compressors losing too much oil, reason to this was leaking oil injection valve on standby comp and it blows all oil from separator through the compressor to the suction line and ended to pump separator (no check valve on suction, only discharge) when both comps was running there was no problems. And this was nh3 system
    Sep 2012
    India
    77
    13
    Re: Oil carry over
    Hi Lync
    Why not install seconday oil separator in series. Are the evaporators flooded design or dry expansion?
    Are the primary oil separators horizontal or vertical?
    In horizontal oil separators there are chances of higher oil carry over in case the oil charging is excessive.
    In case of vertical oil separators there should be enough space (Vertical separation space) in the oil separator for primary separation because of the change in direction, deflection, etc.
    Mar 2005
    638
    Re: Oil carry over
    What is the condensing pressure when the oil is being lost. I bet it is low enough that the CFM at the discharge is over loading the separator elements. Try raising the discharge pressure and see if this helps.
    Ken