    digital scroll



    Hello,

    Digital Scroll: Copeland HLR31 - when the temp. has reached, the compressor don't stop at low pressure (pump down), he stays working in his own capacity regulation.
    Anybody an idea?



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: digital scroll

    what does the suction guage read,have you attached service gauges?

  3. #3
    Join Date
    Mar 2010
    Location
    usa
    Age
    46
    Posts
    120
    Rep Power
    17

    Re: digital scroll

    Im not shure what application you are using it for. The Digital Control works off a Demand Signal of 1-5 VDC. The Compressor Capacity is @ 100% @ 5VDC and unloading between 1.3-5 VDC. The Compressor will shut off when the Demand Signal drops below 1.25 VDC. It will restart when the Demand Signal rises over 1.44 VDC and the Anti short cycle timer ( if applicable) times out. You may have somthing wired incorrectl. The Pressure swithes sould be in the M1-M2 circut.

  4. #4
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: digital scroll

    Thanks for the replay,
    One coolroom with two evaporators, one aggregate with one digital en one normal compressor.
    ***** R507, SET = 2.8 bar ( - 15°C ), When the temp. has reached, the compressor stops about 2 bar, after a little bit, the pressure increases about 2.5 bar, the digital compressor starts and stay running around the SET point and not stop anymore (or after 10 min. or so).
    The min. run time is 0 sec.
    The low pressure setting is now 2 bar, but Copeland Holland advises 1 bar, but with this setting he sure don't stop.
    The wirering is made at Copeland self, I have to bring only the power supply (and the connection condensor).

  5. #5
    Join Date
    Apr 2007
    Location
    lancashire england
    Age
    64
    Posts
    36
    Rep Power
    0

    Re: digital scroll

    on a digital scroll the condensing unit is controlled on pressure which is related to the cabinet temp your lp switch is for safety alll depends on what application you are using it on and what refrigerant you have in your system your digital scroll is only putting hot gas back in to your suction to keep the suction pressure up so it isnt over to big for the application its designed for if only part load is required