    Daikin RZP145DV1 problem



    My Daikin RZP145DV1 suddenly stopped working with no error code. Daikin themselves do not seem to know what is wrong, and suggested replacing all the PCBs and condensor fan motors - an expensive exercise! Is it worth doing this in a step-wise fashion - eg replacing inverter board first, etc or should I just accept Daikin's suggestion? Here is a run down from our A/C tech:


    Switched on AC, set temperature conroller to 30C.
    Checked "SERVICE MONITOR where the green LED is flashing and the 4 red LEDs are off. SERVICE MONITOR saying eveything is normal
    AC goes through its start up procedure, runs for approx. 30s and then shuts down.
    Checked SERVICE MONITOR again where the green LED is flashing and the 4 red LEDs are off. SERVICE MONITOR saying eveything is normal.

    Checked compressor windings for continuity, earth leakage, and current draw. Compressor is fine
    Checked power supply and all connections

    Checked all fuses found good

    Thermisters checked @ 21C ambient

    Checked thermistors R1T 23kohms (24kohms)
    Checked thermister R2T 27kohms (24kohms)
    Checked thermister R3T 284kohms (280kohms)
    Checked thermister R4T 24kohms ( 24kohms)

    Figures in () are the values the thermisters should read at 21C, thermisters are fine

    Contacted Daiken technical support (Mark) discussed my findings where he suggested to also check the condensor fan motors.(CFM)
    Reason being that they are often times responsable for causing damage to printed circuit boards (PCB) on inverter AC.
    I checked both CFMs as per his instructions but could not find any mechanical damage.

    Marks suggestion was to replace all PCBs on the outdoor unit and also the CFM. " Do not replace the PCBs without replacing the CFMs"

    Here is the email from Daiken displaying part numbers and prices:



    DAIKIN SERVICE SPARE PARTS daikinspare@daikin.com.au


    RZP145DV1

    Control 1693498 $570.00

    Resistor 065339J $3.01

    PCB, Inverter 1697320 $407.13

    A3P 1301201 $16.68

    Active Module 1283187 $209.90

    Fan motor x 2 1283194 $218.42each



    Any help will be greatly appreciated!



  2. #2
    Join Date
    Jul 2009
    Location
    stoke on trent
    Posts
    48
    Rep Power
    0

    Re: Daikin RZP145DV1 problem

    You set the controller to 30 ? Is that in cooling mode ?

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin RZP145DV1 problem

    daikin alarms have to go out of range 3 times before they display the fault- check loose connections on the interconnect, ensure no3 signal is terminal block or crimped in the isolator. is this a hardwired controller on it?
    check external condensate pump doesnt have a failsafe contact wired in, pull the drain plug to see if a lot of water comes out,does this only happen in cooling mode?

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin RZP145DV1 problem

    aikin inverters are prone to pressure transducer failing so it thinks its short of gas- its a 3 pin connector and should be a 0 to 10vdc on the black,had a k series that started up for 10seconds then stopped and did nothing,with no alarm codes- spent 3 days checking every failsafe on the system- did have 9 compressors and 30 indoors

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin RZP145DV1 problem

    Does the unit run in Emergency mode?

  6. #6
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Daikin RZP145DV1 problem

    Check for any fault code history
    Last edited by AbsoluteWDJ; 21-07-2012 at 10:41 AM.

  7. #7
    Join Date
    Oct 2009
    Location
    Sydney
    Age
    38
    Posts
    69
    Rep Power
    15

    Re: Daikin RZP145DV1 problem

    i had a very similar unit, an rzp125dv1 do almost the exact same thing. the compressor would start and run for about 10 seconds or so then cut out. turned out it was the suction pressure transducer, the unit thought it was short of gas due to the transducer playing up. do this: take the transducer off the suction line and put it on to a bottle of gas, and see if it runs then. when i did this on the unit i was working on the unit ran beautifully, the compressor ramped up all the way and everything seemed great. when u take the transducer off the unit will likely go straight into fault so u will need to reset it first.

    test the transducer in comparison to daikins specs (available in the service manual) and see what u come up with. when my compressor started up, the unit thought it was pulling a vacuum with the readings the transducer was returning.

    Also do the LEDs on the outdoor pcb light up? sometimes they can help shed some light, as they may help display faults before it shows up on the wallpad.