Results 1 to 2 of 2
Thread: REYQ14MY1B Oil Removal Issue
01-07-2012, 10:05 PM #1
Ok, so i changed a compressor on a VRV 3 and added driers. My boss then told me we have to change the oil to comply with Daikin warranty regs.
I pressured the system up with nitrogen and put the system through mode 21 (open all solinoids)
and opened the oil returning hoping to remove most of the oil, but all i got was nitrogen coming through the oil return valve.
Is there a certain field setting i need to put the unit into to remove the oil or will i have to run it up on full load to get the oil back to the compressors?
The unit is a VRV3 REYQ14MY1B, i took an oil sample from the old compressor i removed and it was literatly black.
Cheers guys.
01-07-2012, 10:44 PM #2
Re: REYQ14MY1B Oil Removal Issue
to remove the oil you should have done it before vaccing the system- daikin do an oil kit that involes pulling a vac on a tin can and sphoning the oil out the other 2 compressors then refill with 3gs then pressure test,vac and charge with the setting mode for opening all valves enabled