    mitsubishi fault



    Has any body come across a fault on Mitsubishi cassette unit U8?



  2. #2
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    45
    Posts
    54
    Rep Power
    19

    Re: mitsubishi fault

    My "k series" manual saya the follwing:

    "U8 is no fault (factory setting)"

    U faults are generally to do with outdoor units,
    has the outdoor unit pcb been replaced and not setup properley????

    does the unit run??

  3. #3
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    45
    Posts
    54
    Rep Power
    19

    Re: mitsubishi fault

    further to my last post

    if the display is actually "UA" or "U6" this is compressor overcurrent

    also if you have confused with daikin (a U8 on their equip is transmission errror between controllers)

  4. #4
    Join Date
    Aug 2001
    Location
    ireland
    Posts
    34
    Rep Power
    0

    Re: mitsubishi fault

    Units runs ok but stops after a couple of days and U8 comes up when you press check button. indoor unit continues to run, press on / off button and it comes back to normal. Have cleared fault on outdoor board.
    Techni

  5. #5
    Join Date
    Dec 2004
    Location
    manchester
    Posts
    95
    Rep Power
    20

    Re: mitsubishi fault

    in the book it says abnomality of outdoor fan motor
    so it it is either the fan motor or the pcb

  6. #6
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: mitsubishi fault

    Hi Techni
    U8 is a factory generated code it means nothin if you press the check button and this shows it means there are no faults in the error history. If the unit is stopping and no fault is showing intermittendly then if its a K series check the control voltage on the interconnecting terminals if the voltage is down around 10 volts DC then when the compressor starts there is a voltage drop and the outboard locks up but no fault shows. Hence the u8 its a difficu;lt one to sort as its the starting draw on the compressor that causes the drop U may have tofit a 12 volt Dc power supply to the outdoor and use the existing control signal to switch some small relays for control. I have also had it when the remote conrrol cable is passing over emrgency lighting in the ceiling the signal gets interrupted by the magnitic field around the power supplies for the lights just reroute the cable if this the case.
    hope this helps
    regards
    T

  7. #7
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: mitsubishi fault

    Excuse the spelling Christmas party last nightIm suffering badly

Similar Threads

  1. Mitsubishi vrv
    By dakesojo in forum Air Conditioning
    Replies: 20
    Last Post: 22-09-2009, 01:04 PM
  2. Chigo Cpa-09co Fault Codes? E4?
    By chigosimon in forum Trouble Shooting
    Replies: 5
    Last Post: 24-11-2007, 12:46 AM
  3. Diplomat 6528 Fault Code
    By Targus in forum Domestic
    Replies: 3
    Last Post: 31-10-2006, 07:43 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •