    Question Zanotti drop in with evaporator fan problem



    Can anyone help with a drop in unit Zanotti unit that states that the evaporator fans are called for on the controll pannel but is not suppying voltage to the fan motors.
    I have no experance with these controllers was called onto job at 7pm this evening noticed the fault and tried to back trace the wireing ( without a guide )only to find two wires only from the controller to the unit.
    This started me thinking pulse width modulation ,no schematic , late , roof built after coolroom and no axcess .......call for help and come back tomorrow
    If anyone can guide me to a site with information in english on these units I would be very grateful.
    Merry Christmas to everyone
    (dont you love it in the tropics)



  2. #2
    Join Date
    Apr 2002
    Location
    Australia
    Posts
    35
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    Yes maybe it was the cool refreshing ale that made me forget to include the model number but it was worth it
    Model number MSB225N60F

  3. #3
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Zanotti drop in with evaporator fan problem

    G'day Cary.

    Could be a control board problem.

    But dont take my word for it
    Ring these people.

    Bromic
    (02) 97483900
    Ask for Gabriella.

    They should know.

    Regards

  4. #4
    Join Date
    Jun 2005
    Location
    U.K.
    Posts
    16
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    hi
    depending what control it has on it more then likely if the temperature on the evaporator has not reach it set temperature the fan won't work that is if it is a zonotti uniblock unit

  5. #5
    Join Date
    Jun 2005
    Location
    U.K.
    Posts
    16
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    hi
    this is more likely low on refrigerant the evaporator fan will not work if the sensor on the coil does not reach the set temperature

  6. #6
    Join Date
    Jun 2005
    Location
    U.K.
    Posts
    16
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    hi cary
    system could be low on refrigerant or faulty exp. valves
    the sensor on the evaporator is not getting the temperature it is set at. first checked the condenser is the temperature hot only on the first few coil if that is the case then it is the exp. valves

  7. #7
    Join Date
    Sep 2005
    Location
    england
    Age
    61
    Posts
    17
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    hi all
    uk agent for zanotti units is afr

    they can be contacted at

    www.afr.co.uk

    i have used them considerably and found them extremeley helpful

    regards to all
    fridge51

    phil thompson
    srvice director
    F T Refrigeration Ltd

    www.ftrefrigerationltd.co.uk
    Last edited by fridge51; 13-12-2005 at 11:29 AM.
    :eek:Why on earth would somebody do that?:(

  8. #8
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Zanotti drop in with evaporator fan problem

    Sounds like either fan relay or defrost probe.
    Takes a licking, keeps on ticking.

  9. #9
    Join Date
    Oct 2005
    Location
    kent , england
    Posts
    27
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    If the fan is indicated as being on on the controller it's gotta be the relay on the board at fault. A new board I guess, unless you're good at soldering & can get hold of a replacement board relay
    chill out it's only a fridge

  10. #10
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Zanotti drop in with evaporator fan problem

    Are you sure there is no door switch?

    Have you checked for a live coming out of the controller?

    Pay for my flight out there and I will come and sort it out for you. Its friggin freezing here.


    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  11. #11
    Join Date
    Apr 2002
    Location
    Australia
    Posts
    35
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    [QUOTE=chillin out]Are you sure there is no door switch?

    Have you checked for a live coming out of the controller?

    Pay for my flight out there and I will come and sort it out for you. Its friggin freezing here.

    Love to oblige with the air fair but I think the customer might buck pitty because it is a wonderful caravan park set in the middle of a rural valley and deer farm you would enjoy a refreshing dip in the Yabba river whilst sipping on an icey cold beer.But enough of the daydream.
    There is a door switch and it seems operable ,the control pannel shows fans called for but there is no supply coming from the relay on the PC Board.
    The suction pressure is 650 kpa (unit running on 404a) when unit is at rest and pressures are equalised and drop down to 220 kpa when running( which seems a bit low to me)I was going to reclaim refrigerant weigh and recharge unit yesterday but a storm caused a blackout and power has only just been restored (28hr).
    The bit that has me confused is even with the fans not operating the evaporator has no ice build up and the suction pipe to the compressor does have an ice covering.
    Planned of action:
    reclaim and recharge
    direct wire the evaporator fans
    check for bypass on the hot gas defrost solinoid.
    Anyone got any other ideas Id be happy to hear.

    You pay the air fair and Ill put on the coldies an prawns

  12. #12
    Join Date
    Apr 2002
    Location
    Australia
    Posts
    35
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    forgot to mention the expansion device is a capillary tube and the fault is supposed to have come on quickly ie within one day.

  13. #13
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Zanotti drop in with evaporator fan problem

    The bit that has me confused is even with the fans not operating the evaporator has no ice build up and the suction pipe to the compressor does have an ice covering.
    How bad is the ice on the suction?

    I had a freezer that had a snapped capillary just where it went into the suction. No cooling on the evap but a big ball of ice on the suction and the comp.

    but there is no supply coming from the relay on the PC Board.
    Are you sure it is ment to give you a supply? Does it not just provide a neutral?

    Can you get a pic of the controller?


    Chillin
    Last edited by chillin out; 14-12-2005 at 07:52 PM. Reason: $hit spelling, but hey who cares?
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Zanotti drop in with evaporator fan problem

    Normally, Zanotti uses Eliwell OEM controllers.
    If the LED is on, then the controller is asking for fans.
    The probes have nothing to see with this.
    If there's a probe fault, you will get a E1 or E2 error.

    So, is relay of the fans on the power PCB energised and
    if so, relay contacts are broken inside the PCB relay.

    Desolder the relay and replace it, the center distances of the holes is allways the same.

    You can measure all this on the backside of the PCB.
    Is the soldering not loosen from the copper lanes on the PCB?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Smile Re: Zanotti drop in with evaporator fan problem

    Zanotti use a basis of Carel controllers (both Italian) the fan relay does (from memory) switch the live feed to the fan/s. the defrost probe will read the evap. coil temp. and after a defrost will hold the fans off untill the coil is down in temp. to the programmed set temp. for fan delay. if the evap/defrost probe is faulty then the fans may stay off even though the fan LED says they should run. the quoted model number means nothing to me as ive not worked on one for some time, but i do remember the eng. code to access parameters is 22 like all early Carel controls. also i seem to remember a secret button for access to stop end users fiddling. i may have a carel-zanotti book at the office so i will check when i get time.

    regards
    Slingblade


    was the austrailian phone number any help (out of interest)?
    Last edited by slingblade; 14-12-2005 at 09:46 PM.
    Takes a licking, keeps on ticking.

  16. #16
    Join Date
    Apr 2002
    Location
    Australia
    Posts
    35
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    Now it just gets wierd.
    Went back to the job this afternoon (only a storage room for softdrinks so all other breakdowns have priorty) and am greated with "so you fixed it before you left".
    Bugger me the room was down to temp unit cycling on temperature setting and evaporator fans working.
    So it seems the high evaporator temperature was holding the fans out.... no problem but what was causing the high evaporator temperature?
    Could not be refrigerant shortage unless some fridge fairy topped it off during the black out.
    Ice clogged evaporator ? I had the evaporator in my hand as I was determining weather it was TX or cappilllary( it was a cap) and could see no ice at all.
    The suction pressure when it was faulting was low (200kpa) now it is a respectable 400kpa and the suction pipe is still showing a light frost back to the compressor.
    Got me wet.
    Do I just take the credit for the fridge fairys work problem is I dont have his/her mobile number for when the call back comes.

    slingback did you mean the number from temprite yes it did work ok they emailed me the programing pramaters unfortunitaly for another model but at least they tried

  17. #17
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Zanotti drop in with evaporator fan problem

    HI, i now suspect you had a restriction somewhere and the lack of liquid flow through the evap. would not drop the temp. this would then stop the fans from running due to high defrost probe temp. the blockage has now cleared (oil in capillary/stuck expansion valve?) and the problem is solved.

    slingback
    That's Slingblade mate.

    cheers.
    Takes a licking, keeps on ticking.

  18. #18
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Zanotti drop in with evaporator fan problem

    What do you mean by " high Evaporator temperature? "
    What was the temperature of the evaporator coil at the time fans were not working
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  19. #19
    Join Date
    Apr 2002
    Location
    Australia
    Posts
    35
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    "
    What was the temperature of the evaporator coil at the time fans were not working[/QUOTE]

    The temp in the room was 14 so I guess the evaporator would have been 10 to 12 degrees.
    The owner has not contacted me to say it has stopped working yet so heres hopeing
    (sorry to slingblade from Lary)

  20. #20
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Zanotti drop in with evaporator fan problem

    It could have been a multitude of reasons:

    Cold Room inadvertently switched off by someone, then restarted

    Post defrost............Drainage time inhibiting fans switching on

    I can guarrantee you.........It was not a fairy!!

    But glad all is working fine
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  21. #21
    Join Date
    Jul 2007
    Location
    UK
    Posts
    9
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    The Zanotti guys in the UK recently took over Hubbard and you can now use their excellent back up for both types of units.
    Try calling 01473 892210.

  22. #22
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Zanotti drop in with evaporator fan problem

    hi there i can more or less garentee that the fault is with either the door switch or a missing link on the pcb where the door switch should be wired in i would check there first

  23. #23
    Join Date
    Oct 2007
    Location
    Belgium
    Age
    58
    Posts
    29
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    Hi guys. I had the same problem twice in a few months.
    I replaced the controller board and the fans worked again. This was on a MSB225T131F unit.

    Eric.

  24. #24
    Join Date
    Apr 2007
    Location
    lancashire england
    Age
    64
    Posts
    36
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    if its zannoti it probably as a carel controller on it go in to the parameters password to parameters is22 go into fan control and put the fans to run continuos or alter the fan deley temp so fans should come on

  25. #25
    Join Date
    Apr 2007
    Location
    lancashire england
    Age
    64
    Posts
    36
    Rep Power
    0

    Re: Zanotti drop in with evaporator fan problem

    there is as lot of answers to this problem not everyone can b right so lets presume iam KEEP IT SIMPLE MOST FAULTS R

Similar Threads

  1. A question about the pressure drop in coil .
    By jackcn in forum Fundamentals
    Replies: 20
    Last Post: 13-12-2008, 05:10 PM
  2. Strange problem
    By Peter_1 in forum Electrical
    Replies: 9
    Last Post: 10-04-2007, 05:19 PM
  3. pressure drop between expansion valve and distributor
    By aygul in forum Technical Speculations
    Replies: 10
    Last Post: 22-01-2004, 09:47 AM
  4. capacity problem
    By Kathleen in forum Trouble Shooting
    Replies: 22
    Last Post: 15-01-2003, 03:13 PM
  5. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •