12-12-2005, 10:37 AM #1
Zanotti drop in with evaporator fan problem
Can anyone help with a drop in unit Zanotti unit that states that the evaporator fans are called for on the controll pannel but is not suppying voltage to the fan motors.
I have no experance with these controllers was called onto job at 7pm this evening noticed the fault and tried to back trace the wireing ( without a guide )only to find two wires only from the controller to the unit.
This started me thinking pulse width modulation ,no schematic , late , roof built after coolroom and no axcess .......call for help and come back tomorrow
If anyone can guide me to a site with information in english on these units I would be very grateful.
Merry Christmas to everyone
(dont you love it in the tropics)
-
12-12-2005, 10:43 AM #2
Re: Zanotti drop in with evaporator fan problem
Yes maybe it was the cool refreshing ale that made me forget to include the model number but it was worth it
Model number MSB225N60F
-
12-12-2005, 11:05 AM #3
Re: Zanotti drop in with evaporator fan problem
G'day Cary.
Could be a control board problem.
But dont take my word for it
Ring these people.
Bromic
(02) 97483900
Ask for Gabriella.
They should know.
Regards
-
12-12-2005, 11:31 PM #4
Re: Zanotti drop in with evaporator fan problem
hi
depending what control it has on it more then likely if the temperature on the evaporator has not reach it set temperature the fan won't work that is if it is a zonotti uniblock unit
-
12-12-2005, 11:40 PM #5
Re: Zanotti drop in with evaporator fan problem
hi
this is more likely low on refrigerant the evaporator fan will not work if the sensor on the coil does not reach the set temperature
-
12-12-2005, 11:45 PM #6
Re: Zanotti drop in with evaporator fan problem
hi cary
system could be low on refrigerant or faulty exp. valves
the sensor on the evaporator is not getting the temperature it is set at. first checked the condenser is the temperature hot only on the first few coil if that is the case then it is the exp. valves
-
13-12-2005, 09:23 AM #7
Re: Zanotti drop in with evaporator fan problem
hi all
uk agent for zanotti units is afr
they can be contacted at
www.afr.co.uk
i have used them considerably and found them extremeley helpful
regards to all
fridge51
phil thompson
srvice director
F T Refrigeration Ltd
www.ftrefrigerationltd.co.ukLast edited by fridge51; 13-12-2005 at 11:29 AM.
:eek:Why on earth would somebody do that?:(
-
13-12-2005, 10:22 AM #8
Re: Zanotti drop in with evaporator fan problem
Sounds like either fan relay or defrost probe.
Takes a licking, keeps on ticking.
-
13-12-2005, 05:41 PM #9
Re: Zanotti drop in with evaporator fan problem
If the fan is indicated as being on on the controller it's gotta be the relay on the board at fault. A new board I guess, unless you're good at soldering & can get hold of a replacement board relay
chill out it's only a fridge
-
13-12-2005, 07:14 PM #10
Re: Zanotti drop in with evaporator fan problem
Are you sure there is no door switch?
Have you checked for a live coming out of the controller?
Pay for my flight out there and I will come and sort it out for you. Its friggin freezing here.
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
14-12-2005, 10:57 AM #11
Re: Zanotti drop in with evaporator fan problem
[QUOTE=chillin out]Are you sure there is no door switch?
Have you checked for a live coming out of the controller?
Pay for my flight out there and I will come and sort it out for you. Its friggin freezing here.
Love to oblige with the air fair but I think the customer might buck pitty because it is a wonderful caravan park set in the middle of a rural valley and deer farm you would enjoy a refreshing dip in the Yabba river whilst sipping on an icey cold beer.But enough of the daydream.
There is a door switch and it seems operable ,the control pannel shows fans called for but there is no supply coming from the relay on the PC Board.
The suction pressure is 650 kpa (unit running on 404a) when unit is at rest and pressures are equalised and drop down to 220 kpa when running( which seems a bit low to me)I was going to reclaim refrigerant weigh and recharge unit yesterday but a storm caused a blackout and power has only just been restored (28hr).
The bit that has me confused is even with the fans not operating the evaporator has no ice build up and the suction pipe to the compressor does have an ice covering.
Planned of action:
reclaim and recharge
direct wire the evaporator fans
check for bypass on the hot gas defrost solinoid.
Anyone got any other ideas Id be happy to hear.
You pay the air fair and Ill put on the coldies an prawns
-
14-12-2005, 11:02 AM #12
Re: Zanotti drop in with evaporator fan problem
forgot to mention the expansion device is a capillary tube and the fault is supposed to have come on quickly ie within one day.
-
14-12-2005, 07:51 PM #13
Re: Zanotti drop in with evaporator fan problem
The bit that has me confused is even with the fans not operating the evaporator has no ice build up and the suction pipe to the compressor does have an ice covering.
I had a freezer that had a snapped capillary just where it went into the suction. No cooling on the evap but a big ball of ice on the suction and the comp.
but there is no supply coming from the relay on the PC Board.
Can you get a pic of the controller?
ChillinLast edited by chillin out; 14-12-2005 at 07:52 PM. Reason: $hit spelling, but hey who cares?
IF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
14-12-2005, 09:10 PM #14
Re: Zanotti drop in with evaporator fan problem
Normally, Zanotti uses Eliwell OEM controllers.
If the LED is on, then the controller is asking for fans.
The probes have nothing to see with this.
If there's a probe fault, you will get a E1 or E2 error.
So, is relay of the fans on the power PCB energised and
if so, relay contacts are broken inside the PCB relay.
Desolder the relay and replace it, the center distances of the holes is allways the same.
You can measure all this on the backside of the PCB.
Is the soldering not loosen from the copper lanes on the PCB?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
14-12-2005, 09:43 PM #15
Re: Zanotti drop in with evaporator fan problem
Zanotti use a basis of Carel controllers (both Italian) the fan relay does (from memory) switch the live feed to the fan/s. the defrost probe will read the evap. coil temp. and after a defrost will hold the fans off untill the coil is down in temp. to the programmed set temp. for fan delay. if the evap/defrost probe is faulty then the fans may stay off even though the fan LED says they should run. the quoted model number means nothing to me as ive not worked on one for some time, but i do remember the eng. code to access parameters is 22 like all early Carel controls. also i seem to remember a secret button for access to stop end users fiddling. i may have a carel-zanotti book at the office so i will check when i get time.
regards
Slingblade
was the austrailian phone number any help (out of interest)?Last edited by slingblade; 14-12-2005 at 09:46 PM.
Takes a licking, keeps on ticking.
-
15-12-2005, 11:05 AM #16
Re: Zanotti drop in with evaporator fan problem
Now it just gets wierd.
Went back to the job this afternoon (only a storage room for softdrinks so all other breakdowns have priorty) and am greated with "so you fixed it before you left".
Bugger me the room was down to temp unit cycling on temperature setting and evaporator fans working.
So it seems the high evaporator temperature was holding the fans out.... no problem but what was causing the high evaporator temperature?
Could not be refrigerant shortage unless some fridge fairy topped it off during the black out.
Ice clogged evaporator ? I had the evaporator in my hand as I was determining weather it was TX or cappilllary( it was a cap) and could see no ice at all.
The suction pressure when it was faulting was low (200kpa) now it is a respectable 400kpa and the suction pipe is still showing a light frost back to the compressor.
Got me wet.
Do I just take the credit for the fridge fairys work problem is I dont have his/her mobile number for when the call back comes.
slingback did you mean the number from temprite yes it did work ok they emailed me the programing pramaters unfortunitaly for another model but at least they tried
-
16-12-2005, 04:48 PM #17
Re: Zanotti drop in with evaporator fan problem
HI, i now suspect you had a restriction somewhere and the lack of liquid flow through the evap. would not drop the temp. this would then stop the fans from running due to high defrost probe temp. the blockage has now cleared (oil in capillary/stuck expansion valve?) and the problem is solved.
slingback
cheers.Takes a licking, keeps on ticking.
-
16-12-2005, 08:28 PM #18
Re: Zanotti drop in with evaporator fan problem
What do you mean by " high Evaporator temperature? "
What was the temperature of the evaporator coil at the time fans were not workingAny opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
-
16-12-2005, 09:01 PM #19
Re: Zanotti drop in with evaporator fan problem
"
What was the temperature of the evaporator coil at the time fans were not working[/QUOTE]
The temp in the room was 14 so I guess the evaporator would have been 10 to 12 degrees.
The owner has not contacted me to say it has stopped working yet so heres hopeing
(sorry to slingblade from Lary)
-
16-12-2005, 11:03 PM #20
Re: Zanotti drop in with evaporator fan problem
It could have been a multitude of reasons:
Cold Room inadvertently switched off by someone, then restarted
Post defrost............Drainage time inhibiting fans switching on
I can guarrantee you.........It was not a fairy!!
But glad all is working fineAny opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
-
30-10-2007, 08:42 AM #21
Re: Zanotti drop in with evaporator fan problem
The Zanotti guys in the UK recently took over Hubbard and you can now use their excellent back up for both types of units.
Try calling 01473 892210.
-
31-10-2007, 08:44 PM #22
Re: Zanotti drop in with evaporator fan problem
hi there i can more or less garentee that the fault is with either the door switch or a missing link on the pcb where the door switch should be wired in i would check there first
-
31-10-2007, 09:38 PM #23
Re: Zanotti drop in with evaporator fan problem
Hi guys. I had the same problem twice in a few months.
I replaced the controller board and the fans worked again. This was on a MSB225T131F unit.
Eric.
-
01-11-2007, 08:37 PM #24
Re: Zanotti drop in with evaporator fan problem
if its zannoti it probably as a carel controller on it go in to the parameters password to parameters is22 go into fan control and put the fans to run continuos or alter the fan deley temp so fans should come on
-
01-11-2007, 08:43 PM #25
Re: Zanotti drop in with evaporator fan problem
there is as lot of answers to this problem not everyone can b right so lets presume iam KEEP IT SIMPLE MOST FAULTS R
Similar Threads
-
A question about the pressure drop in coil .
By jackcn in forum FundamentalsReplies: 20Last Post: 13-12-2008, 05:10 PM -
Strange problem
By Peter_1 in forum ElectricalReplies: 9Last Post: 10-04-2007, 05:19 PM -
pressure drop between expansion valve and distributor
By aygul in forum Technical SpeculationsReplies: 10Last Post: 22-01-2004, 09:47 AM -
capacity problem
By Kathleen in forum Trouble ShootingReplies: 22Last Post: 15-01-2003, 03:13 PM -
TEV capacity related to pressure drop
By DaBit in forum CPU OverclockersReplies: 8Last Post: 06-12-2002, 05:11 PM