    Hitachi RAS 16 FSN



    Hi all

    Today I was working on a RAS 16FSN outdoor unit

    The inverter compressor was found to be faulty, so my workmate altered the dip switches to only operate the standard comp.

    however the standard compressor ran for about 5 minute before stopping and the outdoor shows a 5 r P indication ?
    room temperature remains above 27c

    Does anyone know what the 5 r P means ?
    I have looked at some Hitachi manuals but nothing for that code.
    Tried calling Hitachi Technical a number of times but they have not called me back

    regards

    bob



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Hitachi RAS 16 FSN

    Don't know the units but reading the manual suggests there may be a capacity safety cutting in.

    b. Operation condition
    The constant speed compressor is forced to stop for
    the compressor protection under the condition below:
    Total Capacity of Thermo-ON Indoor Units
    < 50% of Outdoor Unit Capacity
    In case of the above condition, the compressor operates
    and stops repeatedly. This may cause the compressor
    failure. Therefore, the compressor is forced to stop in
    order to protect the compressor.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hitachi RAS 16 FSN

    we have some ras 8,10 fs- when we lose a pot- usually the inverter 1- just disconnect the 3 phase off the terminal block before it goes onto the compressor - so when demand is over 50 % the dol compressor runs happily- for about 18months-then game over- no need to adjust dip switches-as long as the inverter board is ok