    Daikin 4MX80HV1NB probs...



    Hello all,

    I got called out to an r22 inverter 4mx sytem today with a complaint of "it's blowing room temp air"
    Anyway i made sure all 4 wallmounts were calling for cooling and waited, and waited, nothing.
    I checked all the led's and controllers for fault codes, nothing.
    This daikin thinks everything is ok.
    When i pressed the test operation button on the outdoor unit, she fired up and run like a good one.
    In the end, i think i traced the fault. It seems that the outdoor air thermistor thinks todays temperature is below 0degC, because when i rubbed the thermistor to get some heat in it, off she run
    Can anybody offer any tips on how to prove wether the thermistor is at fault or the pcb.
    Can i read the thermistor temp on the controller like i can on Hitachi?
    Can i fit a low ambient kit to this model?

    thanks for any help offered

    cheers

    eggs



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin 4MX80HV1NB probs...

    Eggs

    If you send me an e-mail address I'll send you the service manual in PDF (7.4mb) it's got all the fault codes, thermister values etc in it.

  3. #3
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin 4MX80HV1NB probs...

    Thanks for the book Frank.
    It seems there is nothing wrong with the system.
    Page 38 says cooling mode is designed for ambients of 10to 46 degC below this the outdoor unit may be held of on a safty device.
    And in the trouble shooting section it says it will not run below 0degC.

    Oh dear it looks like my customer has been mis-sold some kit.(not by me, although i did install it sub-contract for a company that has gone bust)

    How do i explain that to them?

    Cheers

    eggs

  4. #4
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Daikin 4MX80HV1NB probs...

    How do i explain that to them?
    Why bother to explain?

    Can`t you get a low ambiant kit for it?

    If you can, just tell the cust that there is a problem and it needs a part. (but don`t tell what part)

    No need to lose face for something you didn`t do.

    Everyones a winner and still friends. (and mabe the chance of more installs)

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  5. #5
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin 4MX80HV1NB probs...

    Quote Originally Posted by chillin out
    Can`t you get a low ambiant kit for it?
    Apparently not

    I spoke to Daikin today and i was told "we no longer offer ancillaries for R22 systems"

    Does anybody offer a "Universal Kit" to suit this system?

    cheers

    eggs

  6. #6
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: Daikin 4MX80HV1NB probs...

    Quote Originally Posted by eggs
    Apparently not

    I spoke to Daikin today and i was told "we no longer offer ancillaries for R22 systems"

    Does anybody offer a "Universal Kit" to suit this system?

    cheers

    eggs
    You will never get such answer from us (Slovak affiliate of Daikin)

    The problem is, that there is no accessory, that could extend the operation range of the outdoor unit.

    As you correctly found the operation is restricted due to the ambient temperature. There is active the software function, that should prevent the compresor against sucting liguid refrigerant during low ambient temperatures.

    The unit is simply designed for the specified temperature range, and unfortunately there is not possible to modify the unit with e.g. fanspeed controller, because this prevention function has nothing to do with condensing pressure.

    What I do not understand, that they have installed a heat pump unit, and they need to cool even at 0°C. This is really aplication problem and the responsibility is on the designer (or the man who proposed the unit) side.

    Unfortunately I have no better answer for you, but maybe better presented than my colleagues you call.

  7. #7
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin 4MX80HV1NB probs...

    Thanks, you have presented it better than my local daikin office

    cheers

    eggs

  8. #8
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Daikin 4MX80HV1NB probs...

    Fit a stat and a timer...job done.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  9. #9
    olsfors's Avatar
    olsfors Guest

    Re: Daikin 4MX80HV1NB probs...

    Hi Frank,

    I have a Daikin 4MX80HV1NB blowing fuses and would very much like to have the service manual for it to be able to fix it. As it is known you are such a nice guy, I have some hope you could email the manual to me. My email address is:
    xxxx

    Many thanks for your help from a pretty cold Switzerland.

    Greetings,
    Jan Olsfors
    Last edited by chillin out; 18-12-2007 at 11:47 PM. Reason: No e-mails allowed to be posted.

  10. #10
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Daikin 4MX80HV1NB probs...

    Remove the outdoor air temp sensor en replace for a resistance of the correct amount for say 15 dgr C! Problem solved!!!!

  11. #11
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin 4MX80HV1NB probs...

    This is a blast from way back!!

    Ha haaaa, i sold them a Tosh mini VRF in the summer!!!!!!!

    Kerching!!!!!!! problem solved.

    And i got £80 from the scrap yard for the old Daikin.

    Eggs

    PS i've nothing against Daikin, i quite like it.

  12. #12
    hrpower's Avatar
    hrpower Guest

    Re: Daikin 4MX80HV1NB probs...

    If is possible send me the service manual for 4MX80HV1NB.

    My mail is helder.rp@gmail.com

    Tank you
    HRPower

  13. #13
    Join Date
    Mar 2007
    Location
    manchester
    Age
    17
    Posts
    63
    Rep Power
    19

    Re: Daikin 4MX80HV1NB probs...

    are daikin really that good??

  14. #14
    avh005's Avatar
    avh005 Guest

    Re: Daikin 4MX80HV1NB probs...

    Yes, they are the marker leaders and always help when they can. Problem is that the R22's is the past and every manufacturer has moved on.

  15. #15
    NFreitas's Avatar
    NFreitas Guest

    Re: Daikin 4MX80HV1NB probs...

    Still anyone have the 4MX80HV1NB Service Manual?
    Thanks

Similar Threads

  1. Daikin Refnet Position
    By puddleboy3 in forum Air Conditioning
    Replies: 15
    Last Post: 13-02-2009, 04:12 PM
  2. New to RE and needing Daikin Help
    By Owen in forum Air Conditioning
    Replies: 20
    Last Post: 25-09-2008, 06:55 PM
  3. Daikin Analyzer
    By marc5180 in forum Fundamentals
    Replies: 10
    Last Post: 02-08-2008, 07:15 PM
  4. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM
  5. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •