    sharp fault



    hey gentlemen.. wonder if anyone can help.. got a split flashing error on led 14 times which is pam over voltage error??. manual tells me to replace control pwb assembly. but noticed comp starts for a couple of secs then goes off. only drawing 5a max so doesnt look seized. but dont want to just order pwb then find out comp has blown board. aski here cause im drawing a blank finding anyone from sharp for support and parts.
    thanks in advance



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: sharp fault

    Follow the link for some manuals. however you don't say which is yours.
    Hopefully it will help?
    Grizzly
    http://servicemanualairconditioner.b...ce-manual.html

  3. #3
    Join Date
    Nov 2008
    Location
    north west
    Posts
    13
    Rep Power
    0

    Re: sharp fault

    cheers for the reply. i managed to get the service manual but it doesnt really go into much detail on the faults. but think the units gettin binned off now. hopefully theyll go fora shiny new mitsi.