    city multi ymfc



    gents- city multi ymfc 410a 2007 outdoor address 58,bc 59 indoors 08-13 all present- sw1 1 2 10 on cannot detect 3 parf27 controllers-which are connected on 08,11,13- checked address on controllers-connected on the m net - 108,111,113- system still alarms on 000 6607
    run it as a stand alone -disconnected the tb7 for the g50- still alarms- all indoor connections ok, outdoor-29vdc on mnet- swapped o...utdoor boards with another unit-changed address on rotary switches ok-still fooking alarms(have done virgin restart- also the g50 was connected to oudoors 51,58 couldnt detect system 58- refrigerant moniter only showed 51 outdoor 52 bc 1-7 indoors and controllers-couldnt detect system 58- tb7 link from 51-58 ok-mitsi suspect power pack on g50!- any ideas? ta



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: city multi ymfc

    Fit a Daikin.....self addresses every time

  3. #3
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: city multi ymfc

    Quote Originally Posted by install monkey View Post
    gents- city multi ymfc 410a 2007 outdoor address 58,bc 59 indoors 08-13 all present- sw1 1 2 10 on cannot detect 3 parf27 controllers-which are connected on 08,11,13- checked address on controllers-connected on the m net - 108,111,113- system still alarms on 000 6607
    run it as a stand alone -disconnected the tb7 for the g50- still alarms- all indoor connections ok, outdoor-29vdc on mnet- swapped o...utdoor boards with another unit-changed address on rotary switches ok-still fooking alarms(have done virgin restart- also the g50 was connected to oudoors 51,58 couldnt detect system 58- refrigerant moniter only showed 51 outdoor 52 bc 1-7 indoors and controllers-couldnt detect system 58- tb7 link from 51-58 ok-mitsi suspect power pack on g50!- any ideas? ta
    I doubt the power pack. You dis-connected TB7 (G50) and you still had 6607? Right?
    Grouping indoor units with the M-Net controller might be the issue. Has the system had any modifications of late?

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: city multi ymfc

    its been in for 4 yrs and was probably modified 2yr ago when the hotel was refurbished-we took over the repairs etc 8mth ago- dont know if its ever worked properly-as the system still operates with the fault code flashing-doesnt help with a site handyman-sticks his screwdriver in anything!- strange how the outdoor doesnt detect 3 controllers on the system- but the controllers work ok? also theres a few covers off the indoors so someones been poking about

  5. #5
    Join Date
    Jan 2010
    Location
    Coventry
    Age
    36
    Posts
    37
    Rep Power
    0

    Re: city multi ymfc

    i thought that sw1 1,2,10 only brought up the bc box addresses?
    Last edited by Reffnut; 17-03-2012 at 09:12 AM.

  6. #6
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    19

    Re: city multi ymfc

    Thats correct
    In the words of David Byrne, Well...How did I get here?

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: city multi ymfc

    sw 1 ,1 and 10 is indoor unit addresses 2,10 bc box address 1,2,10 remote controllers- i checked this on system 51 and all is displayed remotes,indoors and bc, but not on system 58

  8. #8
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: city multi ymfc

    Hi IM, could you please check outdoor units' SW2-1s all should be ON so that your G-50A will decide the grouping of indoor unit and remote controller.
    If SW2-1s are OFF, outdoor unit will decide the grouping.
    I think one of the outdoor unit's SW2-1 is OFF position (may be system 58).
    Hope this help for this issue.

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: city multi ymfc

    sw2-1 is off( centralised controller) for all 8 outdoors- i checked system 51 and that picked up all indoor controllers,the g50 picked this up- with 51 and 58 connected only 51 exists on the g50, both outdoor pcbs were swapped to see if there was an issue,but still problems with 58
    Quote Originally Posted by JoeAT50A View Post
    Hi IM, could you please check outdoor units' SW2-1s all should be ON so that your G-50A will decide the grouping of indoor unit and remote controller.
    If SW2-1s are OFF, outdoor unit will decide the grouping.
    I think one of the outdoor unit's SW2-1 is OFF position (may be system 58).
    Hope this help for this issue.

  10. #10
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: city multi ymfc

    SW 2-1 ON for (all) both outdoor units. And register again in G-50A for groups.
    RC must shown on the G50A, check all the registered groups one by one.
    G01 should shown 001 indoor, 101 remote controller and so on.
    Check all 13 indoor units you have.

    G50-reg.jpg

  11. #11
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: city multi ymfc

    As joe says the g50 wont picpk them up if it doesn't know it has to look for them.
    Programme all units and initialise G50 again.
    Cheers
    Stu