    Mitsubishi RP200YHA-PEARP200GA ducted system



    Guys
    Have inherited 4 of the above systems in a maintenance contract. The systems are cooling an IT room (wrong equipment), the client has had 4 x steam humidifiers installed to up the humidity.
    Does anybody know if the equipment can be modified so we can get more sensible cooling and negate the steamers.



  2. #2
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Mitsubishi RP200YHA-PEARP200GA ducted system

    Solve the Undersized units. Sensible load is too big for these system. In fact IT room should use PFD instead.