I have a Lennox CR33-24F cased down flow evaporator coil, this is a v configuration with the
condensation tray where the two coil meet in the center.
Can I use this evaporator in a up flow configuration?
I really can't think of why it would not work, other than matching the unit to the furnace.
Thank Rod
-
25-01-2012, 06:00 PM #2
Re: v-coil down flow to up flow
Up flow will turn it into flooded evaporator.
I requires different design.
-
25-01-2012, 07:30 PM #3
Re: v-coil down flow to up flow
You will change the refrigerant flow to air flow from counter flow to parallel flow, loose coil efficiency and have TX valve problems, you will need to interchange the coils.
Last edited by Magoo; 25-01-2012 at 07:38 PM.
-
30-01-2012, 04:47 PM #4
Re: v-coil down flow to up flow
This list full of morons.
-
30-01-2012, 05:13 PM #5
Re: v-coil down flow to up flow
Thank you Mr Dogg,
I for one fully agree with you.
A simple way of picking them out is their post count, anything less than about 500 and you have to take their post with a pinch of salt, if it's less than 50 well...
Now for your original question and why people haven't exactly queued up to give you the answer you want.
1. See previous paragraph.
2. The evaporator in your Lennox unit has been designed for liquid refrigerant to be injected in to the bottom row of each coil, as the refrigerant absorbs heat it will evaporate in to gas. This means that as it travel upwards in the coil the refrigerant becomes lighter and lighter.
Now, if you turn this coil upside down the liquid will be introduced at the top of the coil and your mixture travel downwards within the coil.
This is a potential compressor killer which is why the manufacturers avoid it at all costs.
Now, having been involved in several IT room and IT hall refurbishments and faced what I assume is the same challenges as yourself...
The best solution is normally to leave the A/C units as they are but to install external ducting to change the airflows.
Whichever way you decide to go, I wish you the best of luck.
.
-
30-01-2012, 07:50 PM #6
Re: v-coil down flow to up flow
Good reply Viking.......I can't see that we need to add anything else
Rep points addedLast edited by frank; 30-01-2012 at 09:33 PM.
-
30-01-2012, 08:12 PM #7
Re: v-coil down flow to up flow
Hey Bigg Dogg!
Generally with evap coils the air and refrigerant go in opposite directions, so if the air goes front to back through the coil, the coil is piped for the ***** to go from back to front, that way the coldest gas meets the coldest air and the warmest gas the warmest air, this helps with superheating the refrigerant (don't worry about superheat its way complex), with the air being hotter with this flow arrangement you need less evap coil for superheatin' so more can be used to make the room nice and cool.
If you change the airflow from down flow to up flow there is a possibility that it won't work as well as it used to due to both the air and refrigerant going across the coil in the same direction and more coil being needed for superheating.
Your best bet would be to talk to Lennox and see what the coil is designed and rated for.
You do your countrymen a dissevice by being rude and disrespectful on an international forum.Mostly found in Oxfordshire, UK :)
-
31-01-2012, 01:22 AM #8
Re: v-coil down flow to up flow
Hi Chemi,
you and I are morons.
-
31-01-2012, 04:08 AM #9
Re: v-coil down flow to up flow
Hey magoo, "NO" self promotion please!!!!!!!!!!!!!!!!
-
31-01-2012, 10:25 AM #10
-
31-01-2012, 03:23 PM #11
Re: v-coil down flow to up flow
Wow, incredible what people come up with.
Not turning the unit up side down.
No txv, metered.
The coil is in the same position as the down flow configuration, just the air flows the opposite direction.
This coil setup is no different that the V end of a N-coil.
Can anybody come up with a logical reason why this will not function.
-
31-01-2012, 05:28 PM #12
-
31-01-2012, 05:45 PM #13
-
17-05-2012, 03:45 PM #14
Re: v-coil down flow to up flow
In the upflow position, the coil is on top of the furnace.
In the downflow position, the coil is position on the bottom of the furnace.
The evap coil must be placed after the flow of air through the furnace.
Air must passes the furnace before it go to the coil.
-
17-05-2012, 05:49 PM #15