    Trane ECGAH 250 SENSOR



    Hi

    We have a customer with the above chiller showing a sensor fault

    A sensor 3 1/0


    We have tried swapping the sensors around but the fault remains the same, ( There are 3 sensors)

    Resistances between the sensors are similar , Trane want £80 each for the sensors, so we want to be sure to get it right first time

    Anyone know an alternative sensor or has any experience on this fault

    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,712
    Rep Power
    46

    Re: Trane ECGAH 250 SENSOR

    Hi Doc.
    Maybe this explaination will help?
    Grizzly

  3. #3
    acdoctor's Avatar
    acdoctor Guest

    Re: Trane ECGAH 250 SENSOR

    Thanks for that I am even more puzzled !
    think i need to go back to site and do a few tests as that doc seems to refer to a pressure sensor,
    From the schematic info on the unit I presumed the fault was one of the thermistors but maybe its a pressure transducer issue

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,712
    Rep Power
    46

    Re: Trane ECGAH 250 SENSOR

    Doc.
    it's saying either could be present check which, and use parameter limits specified to decide which is the issue?
    It is telling you where to look now instead of 3 options as before.
    Grizzly