Thread: problem

  1. #1
    Join Date
    Jan 2012
    Location
    United States
    Posts
    3
    Rep Power
    0

    Unhappy problem



    Just installed 5 chigo split unit, model: KFR-25W/Db. start heat mode, but a little heat coming out. all the compresor unit was froseen every time working. low gas. To insert gas need to disconnect cable label # 3 in the compresor, to start in cool mode, gas was below 30 psi, just got some gas insede to 40 psi. but now no start in heat mode, just the fan in the compresor work, change to cool mode and just the fan inside work but no the compresor. Any sugestion, this are new unit and is very cool hear ( afganistan).



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: problem

    Recover all refrigerant, evacuate system and recharge with correct weight of refrigerant.

    Ensure that all electrical cables are connected properly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: problem

    HI RAF, things to cheak = is filter clean , is outdoor fan running right way , have you over gasses the system ? have you added the right gas ) what gas is it ? hope you get it fixed quick , sedgy ,

  4. #4
    Join Date
    Jan 2012
    Location
    United States
    Posts
    3
    Rep Power
    0

    Re: problem

    The gas is R 22

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: problem

    Is n3 wire for the reversing valve? Is it too cold to run in cooling mode? Try warming the room air sensor to see it it will run.
    Mostly found in Oxfordshire, UK :)

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: problem

    Funny how they never gave the discharge pressure in heating mode.
    The said they charged from 30psi to 40 psi (with the reversing valve disconnected to allow charging through the suction service valve shraeder). But never any pressure reading on heating mode given, or temps.

  7. #7
    Join Date
    Jan 2012
    Location
    United States
    Posts
    3
    Rep Power
    0

    Re: problem

    Thank for answer's, but need to apply some solution to fixed the problem, let know when I fixed this.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: problem

    Quote Originally Posted by rafca View Post
    Just installed 5 chigo split unit, model: KFR-25W/Db. start heat mode, but a little heat coming out. all the compresor unit was froseen every time working. low gas.
    Why would you think it was low on gas? If the outdoor coil was frozen, then why wasn't it going into defrost mode?

  9. #9
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: problem

    Gary, most defrost controllers for domestics have a minimum run time, to stop them being on constant defrost. So regardless of defrost requirement, they will not do a defrost cycle unless 40+ minutes have elapsed usually.

    Edit: that's assuming the cheap chinese unit has an outdoor thermistor at all. Some don't, mine doesn't.
    But some just defrost based on indoor coil temp as there's no defrost PCB in the outdoor, or any thermistors on a lead to the indoor control PCB, They must just guess on when the indoor coil temp drops low...
    Next step up from that is a flying lead to the outdoor unit for the indoor PCB,
    Only after that, when people are willing to pay more for an a/c, does the magic of an outdoor defrost PCB show it's head
    Last edited by paul_h; 17-01-2012 at 04:17 PM.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: problem

    I have very little experience with heat pumps. On my own system, there is a defrost thermostat which makes at 32F/0C. This initiates a timer which causes the system to defrost 30 minutes later. The timer can be manually set for 30, 60 or 90 minutes.

    In any case, if the outdoor coil is completely frosted the very last thing that would come to mind is low on gas. The first thing would be defrost problem.

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: problem

    I found this manual for it:

    http://www.chigogroup.com/upload/1011/201011111573.pdf

    Defrost info is near the end of the pdf file.