    Daikin REYQ10M7W1B problem



    I am working on a system with a Daikin REYQ10M7W1B outdoor. In heating mode the outdoor unit continually defrosts and the fan coils never achieve a decent off coil temp. The hot gas outlet to the indoor units leaving the outdoor is reaching 65+ degrees C but the return is never any better than about 20C. Would refrigerant shortage make the unit continually defrost? Ambient is only 9C.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin REYQ10M7W1B problem

    Well, it's worth checking the outdoor unit's temp sensors.
    (Ambient air, coils and liquid lines)
    But after you checked them you will have to verify the charge.

    Out of interest, what temperature does the compressor's discharge line get up to when the system is in heating?

  3. #3
    Join Date
    Dec 2008
    Location
    West Yorkshire
    Posts
    63
    Rep Power
    16

    Re: Daikin REYQ10M7W1B problem

    Compressor discharge between 65 and 70C

  4. #4
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin REYQ10M7W1B problem

    The min time between deforsts is 40min, are you sure the system is not entering equalisation due to BS change over requests? usually caused by an indoor sensor being influenced (recirc of indoor discharge air etc).

    Have you checked the discharge pipe temps entering BS boxes and pipe temps entering indoors?