    hi
    I need DX coil software badly which can calculate 3/8" and 5/8" DX coils

    also i have few questions first is


    1. Can we use 1/4" sight glass in liquid line that is 3/4"
    2. We are trying to use DANFOSS EXP VALVE but their ends are of steel and we have refrigerant piping of copper. how is brazing to be done.


    Awaitin quick reply

    [B]Note[/B] I have PSYCHOMETRIC ASHRAE CHART registered version 15 MB. those who have limit of in their inbox i can mail them
    Regards

    Engineer Ali Abbasi


    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  2. #2
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: few questions

    Hi,
    about your questions:
    1. Yes you can, but don't put the sight glass in the 3/4" line, but put in a small line parallel to the major liquid line. (see attachment)
    2. What kind of TEV is it? Is it a TUA (which are in stainless steel but have bi-metal connections for fast and easy soldering to cupper)?
    Attached Files Attached Files

  3. #3
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Thumbs up Re: few questions

    There is a software from USA Coils which they give with thier catalouge (Free). You can design DX coils with it but I found that it is not very reliable.
    If you use 1/4" sight glass in a 3/4" liquid line then you will end up with a large pressure drop across the sight glass which will vaporize some of the liquid.
    Even Einstein Asked Questions

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: few questions

    I have PSYCHOMETRIC ASHRAE CHART registered version 15 MB. those who have limit of in their inbox i can mail them
    I believe this software is coyright protected by ASHRAE, I would not recommend sending copies of this. Especially since you have your name attached to the offer.

  5. #5
    Join Date
    Jul 2006
    Location
    india
    Posts
    3
    Rep Power
    0

    Re: few questions

    Hi,
    I am fresh HVAC engineer.i have PSYCHOMETRIC chart old one (from my college book).pl. fwd the PSYCHOMETRIC ASHRAE CHART to my mail selva_sraj@hotmail.com
    thanking you.
    regards
    selvaraj

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: few questions

    There is an appropriate brazing material for steel to copper lap joint. Ask your supplier for details. Please note that TUBE TXVs have copper plating on the inside of steel.

Similar Threads

  1. Interview questions
    By zimbo in forum Chit Chat & Service Stories
    Replies: 16
    Last Post: 10-09-2008, 10:06 PM
  2. some questions of air source hp
    By Lc_shi in forum Technical Discussions
    Replies: 3
    Last Post: 11-05-2006, 08:58 PM
  3. questions
    By parry in forum Chit Chat & Service Stories
    Replies: 17
    Last Post: 31-10-2005, 08:46 AM
  4. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM
  5. PC cooling project status update + TEV questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 28-06-2002, 04:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •