Results 1 to 3 of 3
Thread: Egelhof Tev's
-
18-10-2005, 07:16 PM #1
Egelhof Tev's
any body know where i can get information relating to factory preset superheat settings on EGELHOF TEWL expansion valves for r404a?
its roughly the same size as a danfoss TE2.
any help would be appreciated,
thanks
-
18-10-2005, 11:42 PM #2
Re: Egelhof Tev's
Try this web page might be of help, i used the RTC type years ago, HRP in U.K used to stock these. Can be stripped and repaired when motor jams . http://www.steefane.com/catalogue.html P.s scroll down this page to e= expansion valves.
Last edited by Snowman123; 18-10-2005 at 11:44 PM.
-
27-10-2005, 07:44 PM #3
Re: Egelhof Tev's
Hi,
I have an old Egelhof catalogue. It states - Superheat Factory setting: 4K static superheat, applies with normal air conditioning range to a bulb temperature of 0 degrees C, applies within low temperature range to a bulb temperature which corresponds to an evaporation pressure of 1bar (according to refrigerant).
If you need any more info let me know