what evap. temperature should i get
hi guys if I have a vertical freezer with a fan evaporator like ones used in restaurants and the temperature I want to get is -20c what is the evaporator temperature should be reached to cool the space to -20 C or in other words where should i start from to check my system health (the superheat the actual temperature of the suction line)
16-10-2005, 08:30 PM #2
Re: what evap. temperature should i get
Hi Duraid,
Why don`t you just stop the evap fan run the system and see if your licked finger sticks to all the evap but not all the way to the compressor?
I know this is a bit rough but it works for me.
chillinIF AT FIRST YOU DON`T SUCCEED.
and go get a cuppa
16-10-2005, 09:02 PM #3
thanks chillin out but what if my fingers sticks on the first half of evap. and not on the second half does that means lack of charge (of course if we supose all components of system are okay)
16-10-2005, 09:12 PM #4
Most likely yes.
Best thing to do then leak test repair leak and vac and recharge
and go get a cuppa
16-10-2005, 11:00 PM #5
Originally Posted by duraid
To achieve cabinet temperature of -20C you need to evaporate at -30 C minimum
Look on your gauges...........is the compressor sized correctly to achieve this??
If you have a full charge of refrigerant.........and the gauge shows -30C , the cabinet will achieve desired room tempAny opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
17-10-2005, 11:16 AM #6
LMFAO. .Engineering, sciences, math, physics and my brain will generate "not responding " soon
17-10-2005, 11:34 AM #7
Laughing My F***ing Arse Off
17-10-2005, 11:43 AM #8
10x Temprite , very nice translation lololol
regardsEngineering, sciences, math, physics and my brain will generate "not responding " soon
17-10-2005, 05:31 PM #9
delta t is got to be 10
17-10-2005, 06:41 PM #10
What your actual suction temperature/pressure will be is determined by where the condensing unit and unit cooler balance. Normally you will be in the range of 5 to 10 dC cooler than your box temperature.
Ken
27-10-2005, 01:39 PM #11
Originally Posted by Temprite
A few posts prior to this someone posted LMFAO, that particular person has now been ejected from the forum.
Botrous asked what it meant and I told him.
I would never make those remarks towards another members comments.
Get you facts right before you go shooting off at the mouth.
31-10-2005, 08:23 AM #12
Delta T should be 5 to 6 deg's. For -20 DegC application the ideal SST is -26 Deg C. ( That is the return suction line temperature at suction header.).
Check the super heat. genearlly we should maintain 8-10 Deg. at Evapoartor suction. For Air conditioning 8 - 12 Deg is ideal.
Tx and regards
Manoj Menon.
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
re ref. circuit
By shsalameh in forum FundamentalsReplies: 5Last Post: 06-08-2007, 12:59 PM -
Q=? h1=? mechanical schematics
By fridg in forum Technical SpeculationsReplies: 22Last Post: 19-03-2006, 01:43 PM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM -
TEV with MOP: how to keep valve body temp above bulb temp?