    Cool Mc Quay 306.3ST With PCO2 reg.



    3 compressors, screw. when 2 are running, all is cool, but when we add the 3rd, the pco gets soooooooooooo slow! we have tried new boards, exp. valve drivers, replaced, swapped... still, when C3 is running, the protocol for some reason slows down, almost no response when pressing buttons.. unit's running, but i don't know if timers etc. is affected by this.. We dont deal Mcquay anymore so we don't get support. Hope someone in here mb can help.
    thanks!



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Mc Quay 306.3ST With PCO2 reg.

    Hi
    what happens if you run c3 and turn c2 off ?
    do you have the same phenomena?
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Mc Quay 306.3ST With PCO2 reg.

    If just c3, something shorting on that cicuit I suspect
    If the World did not Suck, We would all fall off !

  4. #4
    Join Date
    Jul 2009
    Location
    Norway
    Age
    51
    Posts
    5
    Rep Power
    0

    Re: Mc Quay 306.3ST With PCO2 reg.

    SOLVED! We replaced Plan cable with proper screened cable, then we replaced phone cable between display and master pco, now it works like a charm! it was always c3 that made everything slow.
    Thx for input.

  5. #5
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    78
    Rep Power
    13

    Re: Mc Quay 306.3ST With PCO2 reg.

    Replace the software application with a newer ...