    sorry didnt knw wher to post this, but as its an electrical issue....
    i opened the shower switch up as it jammed in the off position and had a funny fishy smell(cue funny comments....) coming from it....and found it 2 b melted,along with both neutrals
    1 of the neutrals popped out very easily....
    also the 1 of the live wires has a black burn strip running down it....
    but the other live wire is ok...
    my question is this....
    could the melting of the wiring be caused by the switch heating up n melting, due to the loose connection, in turn leading to the melting of the wiring ?
    its 2.5 mm twin and earth...so i would have thought its sufficient enough rite ?
    any ideas ? as this is the second time this switch has burned out and im looking for a permanent fix
    cheers
    Apr 2001
    2,099
    27
    Re: shower switch fault !
    2.5MMM ?????
    Youre joking Krupps
    Is it a 8KW shower?
    I think you need to use ,
    Im not sure if its 6mm or 10mm
    Ill check
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
    Sep 2003
    ISRAEL
    72
    4,248
    I have done a whole house electrics in Scotland,
    Used a 10mm wires for the shower water heater.
    No problems for the past 6 years.
    I agree with Marc, there is nothing like a loose connection for a little fire in the house.
    When in doubt about the wires mm, go one or to higher.
    Chemi
    Jul 2003
    leicester
    42
    122
    sorry meant 6 mm lol not 2.5mm i was thinking about something else at same time as writing this.....
    its a 10.5kw electrical shower...
    think iv sorted it now neways....
    gonna run a fresh 10mm cable in and new switch
    Sep 2005
    uk
    499
    10.5 kw is fairly large for a shower. is the switch a proper rated double pole isolator or the ceiling mounted pull cord type as it may not be rated high enough {10500w/240v = 43.75a} for full load.
    5,667
    Hi Slingblade
    It is now required to calculate everything in the UK as either 230v or 400v so your calculated running current (for cable sizing purposes) should be 10500w/230v = 45.65A. Cable sizing should then be calculated on the instalation method in accordance with BS7671
    Sep 2005
    uk
    499
    Quote Originally Posted by frank
    Hi Slingblade
    k, lets try a little experiment. take 1 avo/multimeter {whichever you prefer} and go and find a single phase supply {this can be found inside any domestic plug socket or distribution board}. set your avo to v~ and connect the black lead to the yellow and green cable and the red lead to the brown or red cable. now look at the scale and you'll have your golden number to use for rating any appliance connected to that supply. in my experience it usually is 240 in the uk. BS numbers are all very well and good but i tend to stick to what goes on in the real world. or you could try finding somthing that is rated to 10.5 kw and measure the current draw with an amprobe you may even find i am correct.
    Jul 2003
    leicester
    42
    122
    its a 45amp double pole ceiling mounted pull cord type as far as i remember...but dont qoute me on that...
    thanks for the info guys...
    5,667
    Obviously you guys are not upto date with current regs
    Sep 2005
    uk
    499
    Quote Originally Posted by Krups
    then a connection somewhere is loose. maybe in the switch or possibly in the shower. might even be in the dis board. loose connection= higher current draw= toast!
    sparking24-7's Avatar
    sparking24-7 Guest
    The length of run is also an issue , the longer the run the higher the resistance the bigger the cable needed.Sounds like a loose connection to me, also in respect of the switch you get what you pay for so it is normally senisible to buy a decent make a first, something like crabtree or mk
    Steve
  1. flow switch connection
    By afeef in forum The Trail of Tears
    Last Post: 23-12-2009, 06:55 PM
  2. Diplomat 6528 Fault Code
    By Targus in forum Domestic
    Last Post: 31-10-2006, 07:43 PM
  3. Chiller fault
    By iceman007 in forum Trouble Shooting
    Last Post: 27-06-2006, 06:15 AM
  4. Shower problems
    By pscott898 in forum Chit Chat & Service Stories
    Last Post: 23-05-2006, 06:24 PM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Last Post: 13-05-2006, 07:23 PM