A good Design?
Hy all
After your opinion which is the best cheapper and most modern solution for the next data;
6.freezer rooms x with a total surface 4000 m3 /-22 *C
The rooms are for store frozen products To -17*C
The customer must have the right to use these coldrooms ,for keep refrigerating products if he whant .
To +4*C
Monitoring and heat echangers are required also
Regards
-
11-10-2005, 06:38 PM #2
Re: A good Design?
You are looking to operate the over a fairly wide temperature range. You will need to balance your condensing unit and unit colers at both conditions. The problems you will encounter are:
TXV operation and sizing
DX distributor sizing and coil circuiting.
I regularly design rooms to operate over a range of temperatures, but the wider the range the more problems you will have.
I'd suggest you hire a loacal engineer capable of studying the design.
Ken
-
11-10-2005, 09:16 PM #3
Re: A good Design?
If you use semi-hermetic or hermetic compressors you will need to verify the compressor selection for both extreme operating conditions (lower and higher evaporating temperatures).
The motors may not be capable of sustaining the operating condition for one or the other of the operating conditions.
The condensers will have to be selected for the highest heat rejection capacity.
This is not an application that may work with prefabricated condensing units. At least, I don't think it will as a first estimate. You may have to resort to using an engineered approach with a remote condenser, multiple compressors (with oil recovery system), and suitable sized evaporators and TXV's.
Originally Posted by TXiceman
Similar Threads
-
capillary tube design
By Chris Zahrt in forum FundamentalsReplies: 5Last Post: 04-06-2009, 09:16 PM -
heat exchanger design
By Lc_shi in forum FundamentalsReplies: 33Last Post: 13-03-2006, 09:57 AM -
R507 in an R134a compressor: system design
By DaBit in forum Technical SpeculationsReplies: 17Last Post: 01-05-2003, 09:25 AM -
R134a <-> liquid heat exchanger design
By DaBit in forum Technical SpeculationsReplies: 19Last Post: 10-05-2002, 08:36 AM