    Hello People,

    im a customer receiving a daikin Vrv3 system, and while installing something went wrong with them i didn't understand what it was. and the system lost all of its gas :S, now i looked at things ( im no pro btw ) there was some oil, from where the gas was leaked.

    so my question was to the engnieer, when you recharge do u add Oil or just the gas ??

    and my question here do refrigirant oil gets added alone or it comes with the 410A ?


    thank you



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: help daikin

    The oil would need to be added seperate to the refrigerant. It is sometimes difficult to estimate how much oil may have been lost during a leak. Often a small amount of oil can create a fairly large stain.
    The quantity to be added will need to be calculated carefully as too much oil can cause operational problems, just the same as too little oil.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Dec 2010
    Location
    Palestine
    Age
    36
    Posts
    23
    Rep Power
    0

    Re: help daikin

    so how can we make sure, Service checker should rule it out or ???? how is the best way to approach this ?

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: help daikin

    The Service Checker will be able to record the values at the various temperature and pressure sensors and from that it should be possible to determine which valves are operational etc, however I do not think that you would be able to estimate the quantity or location of the oil within the circuit. This will need careful consideration by your service engineer to estimate the amount of oil that will need to be added.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  5. #5
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: help daikin

    Don't add first, just adjust the refrigerant accordingly. Then you measure or log or monitor the compressor shell temperature in operation mode. Normally in FarEast (ambient 35C) then shell temperature is around 42C.
    Around this temperature, we could say healthy and enough oil. If so hot, then add in.
    However I have no idea Palestine Texas ambient against shell temperature. More or less same I believed. Because working temperatures/pressures should be same. Try this. Hope that will help.