    Fault code Er11? Fujitsu ARTG split ducted a/c



    Hey. Ive got a unit which after being shut off by a simulated power outage, returns an error code ER11 or as its is displayed "00:11 Er" flashing.

    I have two other units which restart, flash the same error code for a couple of seconds then return to normal operation.

    Fujitsu tech support wont be open till monday and I want to try and fix it on sunday. Its in a bank refurb so can only be done at night or weekends.

    If anyone can help that would be awesome..

    Cheers



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,120
    Rep Power
    25

    Re: Fault code Er11? Fujitsu ARTG split ducted a/c

    Have a look here ,It says water level fault
    http://errorcodeairconditioning.blog...and-floor.html
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Feb 2011
    Location
    England
    Posts
    44
    Rep Power
    0

    Re: Fault code Er11? Fujitsu ARTG split ducted a/c

    Communication error between indoor and outdoor unit if memory serves me rite. Indoor board fault last time I had it.

  4. #4
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: Fault code Er11? Fujitsu ARTG split ducted a/c

    if outdoor isolator is off it can also give this fault. loose cables faulty boards.

  5. #5
    costin1's Avatar
    costin1 Guest

    Re: Fault code Er11? Fujitsu ARTG split ducted a/c

    Cmon,... the signal on wired remote controller is 11c, and that is the first thing that apeares at start-up. This is not error.

  6. #6
    Join Date
    Apr 2010
    Location
    australia
    Age
    45
    Posts
    78
    Rep Power
    14

    Re: Fault code Er11? Fujitsu ARTG split ducted a/c

    i have had 3 units on the same site fail on the same code. Fujitsu came out, they replaced some boards under warranty. I think the service tech had no idea as they replace board after board they even tried to blame it on the wiring. May there is a fault in them? If under warranty let Fujitsu worry about it.