    Daikin New Style LCD hard wired Remote controller



    hi all,
    installed a Daikin VRV 3-S system this week ran it up on saturday.

    system works okay currently left in cooling mode. what could not figure out was how to get the system to work in automatic mode. the system is basically a one to one system a ducted indoor to vrv3 outdoor. 2 pipe connections.

    The Controller i am on about is the new one that you get with split systems.

    the modes shown do not show AUTO. just cooling heat fan dry etc.

    was thinking this may be cos vrv3 2 pipe ie refnets would not allow auto mode to work?

    any ideas guys?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin New Style LCD hard wired Remote controller

    tried sending u a manual but im at my 25 meg limit!- i cant see anything relevent to enabling auto function in the setting modes on the controller or the outdoor. is it a brc1d52 controller?

  3. #3
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Daikin New Style LCD hard wired Remote controller

    hi not sure of the model number its the new type remote controller has got LCD screen. If i return back to site will post the model number of remote controller.

    the last remote like this i installed was a month ago the unit was a wall mounted unit and it had an option for swing louvre where this one being ducted does not.

    so for me the remote controller is given the information from the indoor units as to which style of unit. this is why i am thinking because its VRV 2 pipe that it can not have auto mode. but only guessing.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin New Style LCD hard wired Remote controller

    it shouldnt matter as theres only 1 indoor,i fitted 5 vrv3 not s type with 10 indoors on a 2 pipe with 10 indoor controllers . selected the host controller(dedicate a master controller) and that runs in auto mode. i know hitatchi units u have to configure a setng for auto.

  5. #5
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Daikin New Style LCD hard wired Remote controller

    yeah i would imagine its possible to do, just played around with it looked through the controller manual but could not set AUTO mode. prob try daikin if i go back to site then.


    many thanks Imonkey.

  6. #6
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin New Style LCD hard wired Remote controller

    You can set it through the outdoor unit PCB. I assume you know how to make Mode 1, 2 and 3 changes. Follow these steps:

    Enter setting mode 3 (press mode+return for 5 seconds)
    Setting 3 (press set 3 times then return 1 time)
    enable auto (press set 1 time then return 2 times)
    exit setting mode (mode 1 time)

  7. #7
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Daikin New Style LCD hard wired Remote controller

    hi thanks a lot for the info. i now have Auto on the controller. quick question mchild, why is auto not registered on the controller in the first place is it because its a vrv

    many thanks lee

  8. #8
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin New Style LCD hard wired Remote controller

    Quote Originally Posted by moondawn View Post
    hi thanks a lot for the info. i now have Auto on the controller. quick question mchild, why is auto not registered on the controller in the first place is it because its a vrv

    many thanks lee

    Lee,

    Now that you have the auto change over set you also need to set the temp spread between heating mode and cooling mode.

    Not sure why but the VRV-S units are not set from the factory to have auto change over. In fact, I believe I have read in Daikin documentation that the S units can not be set for auto change over. Not sure why they do it this way.

    Glad you got it set.

  9. #9
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Daikin New Style LCD hard wired Remote controller

    hi mchild.

    this was done first the min-max temps. but then realised auto was not listed.

    many thanks lee