    I have been given a job to fit 4 electric heaters each is 2.5kw to a AHU and also have to fit necessary thermostat, however i have never worked on this type of unit and never installed heaters before,

    and help would be appreciated phots of jobs already done etc.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Dunnair LSFP25

    Sadly the Dunnair website doesn't have much useful on it does it?

    Any electric heater needs a control thermostat and an overheat thermostat as a safety backup. The overall control circuit for the heaters needs to be linked back to the AHU so that they cannot be switched on without the fan running.

    The fan should also incorporate a run on timer so that at plant switch off, timeswitch or otherwise, there will be air blowing over the heaters to dissipate any residual heat.

    Are the heaters being staged or are they being fitted in separate ducts?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2011
    Location
    Australia
    Age
    37
    Posts
    9
    Rep Power
    0

    Re: Dunnair LSFP25

    It is a 4 stage each stage is 2.5kw

  4. #4
    joneyjnr's Avatar
    joneyjnr Guest

    Re: Dunnair LSFP25

    Hi,

    most of the units I have seen have flow switchs to confrim airflow as a safetly.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Dunnair LSFP25

    OK, so you need a four stage thermostat, airflow switch, overheat switch, fan run-on timer, four isolators and you'll be nearly there.

    Some documents on electric duct heaters...
    http://www.swift-air.co.uk/E%20H%20B.pdf
    http://www.ehpricedartmouth.com/pdfs...terCatalog.pdf
    http://xinca.com/docs/johnsoncontrols/pau-2.PDF
    Last edited by Brian_UK; 28-06-2011 at 11:13 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Dunnair LSFP25

    a step controller to gradually load up the heater bank and an interlock to prevent heaters from running when cooling is enabled.