    Frosting of evaporator coil



    Hi,
    Any idea what is the usual cause for evaporator coil blocked with ice rendering the system not cold?
    What is the recommended defrost timing and max no. of times within 24 hour.
    Average ambient temperature in the supermarket around 23 to 25 degree C and RH80%.

    Tks,



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Frosting of evaporator coil

    Hi Cofreth,

    The main reason for frost is high humidity inside the case.

    Is there a fan employed for air circulation or is it static one?

    The defrost, is it hot gas or electric?

    The recommended defrost times/intervals, depends on humidity, No of opening times and experience.

    What is the desired temp in the case?
    An iced coil will not cool.

    Chemi

  3. #3
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Frosting of evaporator coil

    Quote Originally Posted by chemi-cool
    Hi Cofreth,

    The main reason for frost is high humidity inside the case.

    Is there a fan employed for air circulation or is it static one?

    The defrost, is it hot gas or electric?

    The recommended defrost times/intervals, depends on humidity, No of opening times and experience.

    What is the desired temp in the case?
    An iced coil will not cool.

    Chemi
    Is there a fan employed for air circulation or is it static one?
    There are 4 fans circulating air within the multi-deck freezer.

    The defrost, is it hot gas or electric?
    Electric Heater.

    The recommended defrost times/intervals, depends on humidity, No of opening times and experience.
    It's a multi-deck low temp showcase with desire temp of -20 degree C.

  4. #4
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: Frosting of evaporator coil

    i feel it would need defrost at least 3 to 4 times a day (24hr period)...

    how is the defrost situated at the moment how many times for how long?... if you dont allow enough defrosts or for long enough time you'll get ice buildup fast...

    with a supermarket too (i'm not a supermarket man persay) but heavy access to cabinets or door not closed properly for long extended periods could cause large ice build up
    "Old fridgies never die, they just run out of gas!"

  5. #5
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Frosting of evaporator coil

    with a supermarket too (i'm not a supermarket man persay) but heavy access to cabinets or door not closed properly for long extended periods could cause large ice build up
    This is true, but, the evap fins should always clear itself. There maybe lots of frost on the walls and ceiling but the defost system should clear any frost/ice from the evap.

    I beleive this is an excuse for an engineer not being able to repair a fault.

    One of the sites I attend has the door nearly hanging off (waiting for the go-ahead to get replaced) and the coil is clear. Granted the rest of the room is like a snowdrift.

    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  6. #6
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: Frosting of evaporator coil

    Quote Originally Posted by chillin out
    This is true, but, the evap fins should always clear itself. There maybe lots of frost on the walls and ceiling but the defost system should clear any frost/ice from the evap.

    I beleive this is an excuse for an engineer not being able to repair a fault.

    One of the sites I attend has the door nearly hanging off (waiting for the go-ahead to get replaced) and the coil is clear. Granted the rest of the room is like a snowdrift.


    It always helps if the system is one which you maintain through a service contract on a regular or semi-regular basis, but 98% of the time people only call you when there is a problem they cannot fix themselves, and by this i mean they'll try to fix it themselves first before ringing.

    Also it often helps if they answer simple questions asked about there fridge/freezer to know what to undo before starting to look for the real problem...

    At the humidity implied it wouldnt take long for the coil to start icing especically in a freezer coil, this would only be amplified by not enough defrosts to clear coil, or if the defrosts are timed rather then DTT controled not timed long enough to allow for all the ice to be wiped off the coil.

    Could also be a dead or half dead element, was the element tested?

    Also lets face it, being a supermarket, people shopping dont pay the electricity bills and often open the doors for exessive times whilst looking for what they want rather then waiting until they know what they do want, It all helps to amplify the problem.
    "Old fridgies never die, they just run out of gas!"

  7. #7
    Dns's Avatar
    Dns Guest

    Re: Frosting of evaporator coil

    Hi,

    Seems to me that you are talking about Air-conditioning system?
    The reasons may by as follows:-
    1. The Evaporator fan might not be working.
    2. Evaporator coils dirty.
    3. Not enough refrigerant.

  8. #8
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Frosting of evaporator coil

    Hi Dns,
    Are you also doing refrigeration equipment here?

  9. #9
    Join Date
    Apr 2001
    Location
    Southern England
    Age
    66
    Posts
    123
    Rep Power
    24

    Re: Frosting of evaporator coil

    And again make sure the drain line is clear and has a P trap or all that nice warm wet air just rushes back in....
    Derek

  10. #10
    Join Date
    Jul 2005
    Location
    India
    Age
    58
    Posts
    5
    Rep Power
    0

    Re: Frosting of evaporator coil

    Hi..

    Do the system having automatic defrost termination?. If so you can fix 30 mts X 4 times/24Hrs. Even though you have to monitor the frost thickness in 2-3 days. If 30 mts is not suficient then you have to increase 5 more mts. you have to continue till you gets correct time. The amount of frosting will be defferent in all defrosting cycle. for egsample frosting at mid night will be less. early morning will be hardly anything. If defrost termination ( when the coil temperature reaches +ve, the the compressor should stsrt automatically) is not provided it is highly defficult to adjust defrost. More duration will lead high heating and less duration will lead high frosting.

  11. #11
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Frosting of evaporator coil

    I have 6 times a day every time last for 20 min and during defrosting, the solenoid valve is shut, but the evaporator fans are still running. It takes a long time to pull down to require temperature after defrost, sometimes triggering the high temperature alarm in the middle of the night, whoever on duty will need to attend to it.

  12. #12
    Konrad Knoesen's Avatar
    Konrad Knoesen Guest

    Re: Frosting of evaporator coil

    Hi Cofreth
    Sounds like you are using an electronic controller here.Being a freezer you dealing with,the controller should be equiped with two sensor probes,one for temperature and one for defrost.The defrost sensor could be faulty,giving false readings and preventing a defrost cycle from happening.You should re-configure the parameters,especially the alarm delay.Could be the controller going faulty as well.Hope the info helps....

  13. #13
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Frosting of evaporator coil

    Quote Originally Posted by Cofreth
    I have 6 times a day every time last for 20 min and during defrosting, the solenoid valve is shut, but the evaporator fans are still running. It takes a long time to pull down to require temperature after defrost, sometimes triggering the high temperature alarm in the middle of the night, whoever on duty will need to attend to it.

    He says.....................6 times a day and fans run..........so its on a forced air defrost

    I believe the coil is not completely defrosting...........
    Fit electrical heaters to unit

    Give us some more info
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

Similar Threads

  1. Frosting Over Problem In Domestic Fridge
    By Leisure in forum Trouble Shooting
    Replies: 7
    Last Post: 26-08-2006, 01:52 AM
  2. Bosch No Frost Fridge is frosting HELP
    By cooper1258 in forum Domestic
    Replies: 1
    Last Post: 22-08-2006, 11:48 PM
  3. Frosting Over Problem In Domestic Fridge
    By Leisure in forum Trouble Shooting
    Replies: 0
    Last Post: 23-07-2006, 03:52 PM
  4. Frosting in an evaporator
    By Friobernal in forum Technical Discussions